If Zs is acceptable using the armour, can the CSA be unacceptable?
I.e. does the copper equivalence apply to a CPC?
I would think that in most circumstances the armour in a 2 x 10mm^2 SWA is likely to comply as a cpc.Whatever, I did not really intend to get involved in a discussion at this degree of detail. I was merely pointing out that it is not a foregone conclusion that the armour of SWA will always be adequate as a CPC, and I imagine you probably agree with that, don't you?
Of course it can, as it must be able to withstand the fault current until disconnection occurs. A satisfactory Zs does not prove this.If Zs is acceptable using the armour, can the CSA be unacceptable?
If Zs is acceptable using the armour, can the CSA be unacceptable? I.e. does the copper equivalence apply to a CPC?
As Risteard has said, an acceptable Zs does not necessarily guarantee that the material of the conductor will 'withstand the fault current'. Zs is just about whether the fault current will be high enough to operate the OPD within the required time - the CPC's capability of 'withstanding' the current is down to an adiabatic calculation, which will depend upon the material.Perhaps my wording was not ideal. Does the copper equivalence apply to CPCs? That is - does steel not withstand fault current as well as copper of the same CSA? It is not the same as the rule for bonding.
In fact, "the CSA of the armour will be (about) 8.5 times greater than that of copper with the same resistance" is a general truth, regardless of whether the Zs is acceptable or not!Yes but if the Zs is acceptable then the csa of the armour WILL BE 8.5 times that of copper with the same resistance.
I'm not sure I understand your point - as above, my point is that resistance is not necessarily the limiting factor for CPCs, any more than it is bonding conductors.My point is that the copper equivalence does not apply to CPCs as it does for bonding where the resistance of the conductor is not the relevant factor.
My point is that 'copper equivalence' does not apply to CPCs which you said and which prompted my original post.I'm not sure I understand your point - as above, my point is that resistance is not necessarily the limiting factor for CPCs, any more than it is bonding conductors.My point is that the copper equivalence does not apply to CPCs as it does for bonding where the resistance of the conductor is not the relevant factor.
Re: using armour as CPC.provided armour Cu equivalent CSA is adequate
As I said, there is "copper equivalence" and "copper equivalence", but one way of looking at it is that both have to be satisfied for a CPC. One can say that the "copper CSA equivalent of SWA in terms of resistivity" has to be adequate to satisfy Zs requirements, and that the "copper CSA equivalent of SWA in terms of adiabatic performance" has to be adequate to satisfy the adiabatic requirements.My point is that 'copper equivalence' does not apply to CPCs which you said and which prompted my original post.
See above.Re: using armour as CPC.provided armour Cu equivalent CSA is adequate
Maybe, but ISTR that some people, including some electricians, who have good understanding still favour not relying on the armour.The idea of using a copper core as the CPC in SWA seems to be a fairly new idea and I've no idea why people have started doing it. Maybe another knock on effect of DIs who don't know / understand any better?
Fair, enough - but, playing devil's advocate, you are presumably not in the habit of installing T+E which has a CPC made of a relatively high resistance material, which is potentially subject to corrosion and often installed in a hostile environment or achieving electrical continuity with it by means of "plumbing fittings"!I'm not in the habit of running an extra earth with every twin and earth cable I install, nor am I with SWA.
Fair enough.It's been industry standard since SWA was introduced to use the armour as the earth and still is on all commercial and industrial sites unless the adiabatic requires an additional earth. ...