Do you know whether they are 'electronic'? They do not appear to have 'functional earths'.
However, how are you testing them? If with the test button, I imagine that, depending on how it is wired, that might not 'work' in the absence of a neutral.
There are no functional earths. I do not know whether they are electronic inside as I have not opened one
With the neutral disconnected they will not trip with test button, high current loop test, n-e insulation fault present, borrowed neutral to another circuit present, or even back feed from another circuit present on the output!
That sounds fairly comprehensive! With no neutral, there will obviously be no current through the N side of the RCBO, so that any current (>IΔn) through the L side ought to result in a trip - and at least some of scenarios you mention would achieve that.
The mechanical RCD's i.e. Wylex ones, have an advantage of not having to be removed before a megger test takes place, unlike the delicate electronic ones.
And if you take care how you apply the test, electronic ones can be left in place for IR with only a small amount of disconnecting of conductors necessary
Indeed so. In fact, given the uncertainties about which (whether all or otherwise) are 'electronic', it would seem sensible to treat them all as if they were.