- Joined
- 1 Apr 2016
- Messages
- 180
- Reaction score
- 1
- Country
Have you carried out a gas rate?
I wonder if the weir cup you are using is worn.
As I've already said about 10 times I don't touch anything to do with gas
So we are 1 degree out, which may or may not be down to your measuring instrument.
Let me get my slide rule and scientific calculator out and try and see where it's all gone wrong.
You're really don't get it done you. Most instruments tend to go out on their zero but maintain their linear scaling.
For example my thermocouple could have a zero error of -1. It would read -1 degrees at 0 degrees and 99 degrees at 100 degrees.
It could also have a zero error of +1. You just end up with an offset. Both of these thermocouples would still measure the temperature rise just fine because I am only interested in the difference between my incoming water and my DHW. The actual temp readings are irrelevant.
Eh?No you haven't. What results have you seen on a 24kw boiler? Or any boiler
As I've already said about 10 times I don't touch anything to do with gas![]()
Oh but I do get it, I really do.
What I don't get is the reason you're making such a fuss over the results of your totally irrelevant experiment.
The reason no one else has done it is it proves absolutely nothing.
You'd be better off treating yourself to a years subscription to razzle and some kleenex.
You seem to be an authority on the subject which is why I am asking for advise...
So a gas rate requires a RGI?
Eh?
As I said before. Every time I go to diagnose a combi boiler where customer says hot water is not as hot as usual. I do a gas rate. Check flow rate and check temperature differential. Basic tests to diagnose the problem
I don't have a record of the results but last one I repaired it was nothing to do with the boiler. Turned out to be a passing shower valve.
Do they normally the specified rise when in good working order?
do you do if the flow rate isn't at that what is specified in the manual? Mine is rated @ 35 degrees 9.4 l/min but I only get 8 l/min
Some boiler manufacturers quote flow rate at 35 degree rise because it is industry standard. But they actually fit a flow restrictor to give you a 40 degree rise
YesDo they achieve their stated rise though? When new or in good order?
We doI just assumed you guys would do this kind of thing to check out how a boiler is functioning.