Hi, looking for some advice on RCD discrimination please.
Incoming mains goes via the meter and splits to feed 1 consumer unit for one section of the house and another feed goes via a switch that holds what looks like a single BS1361 fuse (60A – too high I think as 10mmsq t&e not clipped direct for the whole run). This feeds a second consumer unit in a different part of the house.
The second consumer unit currently has no RCD protection. Some new circuits need to be added to the second consumer unit and it makes sense to change this CU to a 17th edition dual RCD type plus use RCBOs in the high integrity positions for circuits that would benefit from being separately protected such as shed / workshop / utility room feeds.
Changing the 2nd CU gives the required results – capacity for extra circuits and RCD protection arranged to minimise safety & inconvenience issues.
The issue is that the feed to the 2nd CU is not RCD protected and I assume this would need to be updated at the same time? Mechanical protection of the feed cable isn’t practical, but protecting it with a standard 30mA RCD would introduce all the safety and inconvenience problems present back in the days of a single RCD protecting the whole installation.
Replacing the existing 60A BS1361 fuse with a type S RCD and 45A MCB would seem to be the best overall solution, but doesn’t seem to be compliant from what I can see – any ideas on options greatly appreciated please??