We don't really want to get into the discussion of "being a majority does not mean that you are right".
I'm not suggesting that we do.We don't really want to get into the discussion of "being a majority does not mean that you are right".
Perhaps I have not been saying so i n so many words, but that's how I've always interpreted 530.3.4. In other words, I have assumed that "... a consumer unit incorporating components and protective devices specified by the manufacturer complying with BS EN 61439-3, including the 16kA conditional short-circuit test described in Annex ZB of the standard." is a somewhat more detailed description of what you are calling a "type-tested CU". ...FWIW (and this is not a reply to any person or post), if this is accurate http://www.theiet.org/forums/forum/messageview.cfm?catid=205&threadid=30732&highlight_key=y ) it is not that BS 7671 contains an exemption under some circumstances from the 16kA requirement, it is that type-tested CUs are conditionally rated at 16kA.
Surely one can have CUs which are type-tested and which genuinely have 16kA devices, and thus not need the conditional rating?although, of course, in BS7671-speak, "type-tested" is theoretically redundant, since "a Consumer Unit" is required to be 'type tested'. I suppose that the Part 2 definition of CU really ought to contain a reference to the conditional 16KA test.
In theory, one obviously could. What I'm far less sure of is whether there are any off-the-shelf DBs sold as "Consumer Units" which contain 16A devices.Surely one can have CUs which are type-tested and which genuinely have 16kA devices, and thus not need the conditional rating?
Yes you have. They will be described as conforming to BS EN 61439-3, which requires type testing. There is no need for the manufacturer's description to single out one of the provisions of that standard.despite all the talking we do about "type-tested CUs", in relation to BS7671, I'm not sure that I have ever seen one for sale described as such, let alone labelled as such
Indeed - but, as you've pointed out, virtually anything requires 'type testing'.Yes you have. They will be described as conforming to BS EN 61439-3, which requires type testing.
Maybe not from the manufacturer's viewpoint, but those who wish to take advantage of the second option in 530.3.4 presumably need to know ... or are you perhaps saying that, if it doesn't contain 16kA devices, then it must have undergone (and passed) that conditional short-circuit test in order to conform with 61439-3?There is no need for the manufacturer's description to single out one of the provisions of that standard.
Thanks. I must say that I don't recall having noticed the 'including Annex ZB' bit in any I have looked at - but maybe that's a memory problem! As I said before, I presume this implies that the devices are <16kA, since if they were 16kA, there presumably wouldn't be a need to do a 'conditional' 16kA test. In what you posted, there is no mention of the breaking capacity of the devices - unless that is implied by the Standards cited in relation to the various devices.A lot (if not all) do say 61439-3 and Annex ZB plus other conditions.
That is also very interesting, and I wonder why they say it? Given that I imagine that the same devices (other than the main switch) are probably used ('horizontally') in 3-phase boards, I suspect that it's not them that result in that instruction. Is it perhaps about the IP rating of the case (since 'top surface' requirements differ from the others)? At the start of the thread I did look at the instructions for several CUs, but found none which said anything about orientation, but I may not have looked at Hager.Note the bottom line of this capture - although everyone has probably forgotten that bit of the thread.
Maybe they only do their tests (whatever they are) in the horizontal position?That is also very interesting, and I wonder why they say it?
All it states is:I presume this implies that the devices are <16kA, since if they were 16kA, there presumably wouldn't be a need to do a 'conditional' 16kA test. In what you posted, there is no mention of the breaking capacity of the devices - unless that is implied by the Standards cited in relation to the various devices.
Yes, that is probably the most obvious explanation, and the "why?" of that could be due to the fact that so few people will want to use them vertically. In passing, I recently wrote ...Maybe they only do their tests (whatever they are) in the horizontal position?
On reflection, that may not be true - since if they are not 16kA devices, they are probably not used in 3-phase boards.... Given that I imagine that the same devices (other than the main switch) are probably used ('horizontally') in 3-phase boards, I suspect that it's not them that result in that instruction.
Yes, possibly - in fact, if you will recall, that was the one and only reservation I voiced in relation to vertical installation.Perhaps they feel that the lid will not self-close unless the CU is horizontal?