H
Hot&Cold
Electrician fitted these supposedly brand new sockets and switches waiting to be tiled around.
Thank you.. will tell them to correct them.
Time to hire someone reputable.
ChiTao,any updates ?
If it is not allowed, then surely there cannot be any explicit prohibition.Generically a ring final circuit using 2.5mm² cable and a 30/32A protective device is not allowed by BS 7671. It contravenes the requirements of 433.1.1. Nothing may be supplied by it because you may not have it. Everything is explicitly prohibited from being supplied by it.
I'm temporarily away from my BYB again, so I can't quote chapter and verse, but the regs do address the question of conductors in parallel.If it is not allowed, then surely there cannot be any explicit prohibition.
More importantly, how do you interpret 433.1.1 to two 2.5mm² conductors in parallel?
Yes, I seem to recall that. In any event, as I said, if the two conductors are different lengths (as in ring final, other than at the midpoint), then one of the conductors leg of the ring can carrying anything from ~0% to ~100% of the total load current, depending on the relative lengths [position of load(s), in the case of a ring]. 433.1.204 implicitly makes the assumption that, if the circuit is 'fully loaded' the positioning of loads will be such that no more than two-thirds of the current will flow down one arm (CCC=20A, OPD=30A) - but that obviously is just an 'assumption'.Conductors in parallel must run together.
And, as JW2 recalls, be of pretty much the same length.Conductors in parallel must run together.
Well, in a literal sense it obviously is (a circuit with parallel conductors) - but it is not the scenario addressed in BS7671 of parallel conductors which are 'almost the same length & running together'.And, as JW2 recalls, be of pretty much the same length. So a ring final is very much not a circuit with parallel conductors.
But it is considered to do so in BS7671 - as you went on to say, "433.1.204 implicitly makes the assumption that, if the circuit is 'fully loaded' the positioning of loads will be such that no more than two-thirds of the current will flow down one arm (CCC=20A, OPD=30A)". Looking at the topography of the three RFCs in my house, that seems a realistic assumption.Stillp's question suggests that he was hoping that the presence of two 2.5mm² legs of a ring would increase the effective CCC - but, as I've said, in the 'worst case' virtually all of the load current would flow through just one of the 2.5mm² legs.
Do the electrons know that?Conductors in parallel must run together.
Yes, and that will very often be the case - but it's only an 'assumption' and it might only take one double socket very close to the CU to change things (if you believe that a double socket can supply >20A!). It's true of nearly all, but not quite all, of the ring finals in my house. The one exception which comes to mind is a (reasonably lengthy) ring final which has a double socket less than 1 metre from it's CU in my utility room.- as you went on to say, "433.1.204 implicitly makes the assumption that, if the circuit is 'fully loaded' the positioning of loads will be such that no more than two-thirds of the current will flow down one arm (CCC=20A, OPD=30A)". Looking at the topography of the three RFCs in my house, that seems a realistic assumption.
No, but you can't use the rules for conductors in parallel for a ring circuit.Do the electrons know that?![]()
Of course not, but the conductors are, electrically, in parallel, and the authors of BS7671 seem to have decided that it is acceptable to assume that the shorter conductor may be considered to carry not more than 75% of the total current.No, but you can't use the rules for conductors in parallel for a ring circuit.![]()
But what is the probability of that happening, and for long enough to cause a problem?I could undoubtedly 'overload' that very short bit of cable with that one double socket if I really wanted to!
They seem to have decided that such will usually be the case but, given that the regulation says nothing about the topology of a ring or the distribution of loads, they can't be sure that it will always be the case.Of course not, but the conductors are, electrically, in parallel, and the authors of BS7671 seem to have decided that it is acceptable to assume that the shorter conductor may be considered to carry not more than 75% of the total current.