- Joined
- 27 Jan 2008
- Messages
- 29,384
- Reaction score
- 3,613
- Location
- Country
Simple question is it permitted to have a BS 1363 socket when the circuit is protected by a over current device larger than 32A?
For farms I know the protective device was reduced in size to 20A (705.553.1) but if some one wanted to run a ring final with 4 mm² cable could they protect it with a 40A MCB or is 32A maximum for any circuits with BS 1363 devices fitted?
BS7671.2008 said:433.1.5 Accessories to BS 1363 may be supplied through a ring final circuit. With or without unfused spurs, protected by a 30 A or 32 A protective device complying with BS 88-2.2. BS 88-6. BS 1361. BS 3036, BS EN 60898, BS EN 60947-2 or BS EN 61009-1 (RCBO). The circuit shall be wired with copper conductors having line and neutral conductors with a minimum cross-sectional area of 2.5 mm² except for two-core mineral insulated cables complying with BS EN 60702-1, for which the minimum cross-sectional area is 1.5 mm². Such circuits are deemed to meet the requirements of Regulation 433.1.1 if the current-carrying, capacity (Iz) of the cable is not less than 20 A and if. under the intended conditions of use, the load current in any part of the circuit is unlikely to exceed for long periods the current-carrying capacity (Iz) of the cable.