Fixit was talking about the heating side only.None of what your saying makes sense.
If it’s not zoned why would it share a return pipe.
It can only be the return being shared. It wouldn’t work otherwise.It is zoned. Three zones and a separate zone for the water. It is the return that appears to be shared.
I really don’t understand what you mean. Am I missing something here?Fixit was talking about the heating side only.
I suppose you mean the OP melross who said that. I assume a zoned system has an automatic valve to isolate each zone (and other controls, eg roomstat). That's what I meant when I said if all the valves are closed I can't see how this unwanted flow can happen.He said there are 3 zones and a zone for the hotwater. They share a return pipe in order to save space. But when the zones are off on the room stats/ the heating comes on the radiators still get hot.
I feel the problem may lie with the wiring.
The house I described is non-zoned (no auto valves apart from the 3-port valve, Honeywell W-plan). The boiler is in the kitchen, ground floor. The return from the HW cylinder comes down from the ceiling. The common return from the upstairs rads also comes down from the ceiling. The common return from the downstairs rads comes up from the floor. Originally the upstairs rads return and the HW cylinder return were commoned, then the downstairs rads return came in - problem! Modified to common the rads returns, then the HW cylinder return comes in.A non zoned system would obviously only have one return pipe. There would be no control. The only control would be the boiler stat.
Melross Have you tried this simple test? It will tell you if the problem is caused by the way the returns or connected or by something else, e.g the wiring.You can check if this is the case by feeling the radiator pipes. When a zone is working normally one pipe will be hotter than the other. If, when the zone is turned off, water is entering through the return, the roles will be reversed: i.e the hotter pipe will become the cooler and vice versa.
I assume the system has 4 auto valves, one to each CH zone, one to the HW circuit, the boiler/pump starting when any one or more calls for heat. If a CH valve has failed open, clearly that circuit will get hot whenever any of the other 3 calls.Rads may still get hot when hotwater circuit is calling for heat. With a wiring issue this could cause heating zones not to close. He may not have noticed due to the colder weather and heating being on more frequent but know it’s getting milder the problem becomes more
To add to the above post - what happens if it's piped wrong is the HW return entering the other pipe has 2 ways to go - the "right" way, to the boiler, or the other way, through one set of rads in the reverse direction, then the other set in the forward direction and back to the boiler. If you do a sketch you can easily see it.I assume the system has 4 auto valves, one to each CH zone, one to the HW circuit, the boiler/pump starting when any one or more calls for heat. If a CH valve has failed open, clearly that circuit will get hot whenever any of the other 3 calls.
But (having thought about it again) if any of the CH zones has more than 1 rad, the returns on that zone must still be commoned before the HW return. If, for reasons of layout, the CH returns are brought local to the boiler, or the HW return is close to the rads, that may not be the case, resulting in a problem like I had. If that is the case, it might have happened because it made the plumbing more convenient, and the consequences weren't considered.
OK, keep us posted!Thanks so much for all your comments. I don’t think it will be possible for me to draw a schematic as I’m not technical and there are many long pipe runs It’s a large installation. The technician is returning later today and I plan to show him all your comments. The installation hasn’t been commissioned yet and won’t be until it is working as it should be. Thanks again all, very helpful indeed.
Highly unlikely IMHO.Quick update. Technician been back in touch. One solution he wants to try is fit a less powerful pump as he feels he has over-sized the current pump. Not sure if this is the right solution or not? We have 21 rads and a very long house so I would suspect we need a fair sized pump. We will see!
If he was a knowledgable "technician", he would have calculated the flow and head of your system and sized the pump correctly.Technician been back in touch. One solution he wants to try is fit a less powerful pump as he feels he has over-sized the current pump.
I agree no way. I’m guessing he said the pumps that powerful it pushes passed the zone valves?Highly unlikely IMHO.
If he's from the installers, I would ask (or demand!) his firm produces a schematic. If they can't, because they don't know how they plumbed it, that says something.