I think in 20 years I have yet to find a Competently installed Alpha![]()
Whats your point here? Is it that Alpha boilers need some sort of special installation techniques that confuse people, or the type of people that install Alphas are incompetent?
There is nothing special about Alpha boilers. However, they were cheap. And usually slung at the wall due to one or both parties being incompetent or tight.
Either get the fed and vent altered. Or relocate the pump to the boiler return.
Yes, but remember it needs to be controlled by the boiler.
But the OP's CD24R has an output of 23.5kW and is designed for a differential of 20C. The boiler loss, which you estimate at 1m is nearer 2.5m at full output, assuming a 20C differential. This would rise to about 6m if an 11C differential is used. So your estimates are way out.I estimated it from my system, before I'd seen the data for the Alpha CD24R.
Flow 1.15m3/h, for 11°C rise at 15kW.
If the valve is open, even half a turn, it is acting as a bypass sending water straight back to the boiler without going through the rads or HW cylinder.We do have a system bypass that links from the flow back to the return before the two 2 port valves.
The 15mm pipe isn't the bypass, as I can see the bypass separately. That is also a 15mm pipe, but that goes from flow to return before any of the 2 port valves, and has a manual red handled isolation twisty thing on it, its open by about 2 or 3 turns from closed.
As I said, those estimates were based on my system. For 24kW and 20°C rise the water flow is just over 1m3/h, lower than my 1.15, so the pipe and rads loss is lower. Yes the boiler loss is higher than I used, so the pump differential is higher, but that doesn't affect the pressure rise at the vent connection, which is the main thing I was estimating. Also, as I acknowledged, my estimate of 1m at that point must be too high, as unless he has an unusually high vent pipe loop it would be pumping over continuously. Of course it's impossible to make accurate estimates without knowing more details of the system.But the OP's CD24R has an output of 23.5kW and is designed for a differential of 20C. The boiler loss, which you estimate at 1m is nearer 2.5m at full output, assuming a 20C differential. This would rise to about 6m if an 11C differential is used. So your estimates are way out.
I got confused and thought that the bypass was something separate from the 15mm pipe with a gate valve on it. You should replace the gate valve withIts a manual red turny handle type bypass, not automatic.
The short parts list at the back of the installation manual shows one hex for the 13kW and 18kW, with a different hex for the 24kW version. So your surmise appears correct. Alpha should publish two curves, not one.The Alpha instructions are a bit odd in that only one flow is used, which relates to 18kW. It doesn't say whether the same curve applies to all models, so to use higher flow/pressure drop for 24kW, or the h/ex size varies with boiler rating, when a different curve would apply for each.