Oh - that's a bit further than I had expected. If that's the case, then the houses at the other (closer) end presumably must have very low impedance TN-S earths - lower than many a TN-C-S one.About 20 or so terraced houses away.
One does hear oif the very low Ze figures ...I've had some very very low Zs's, on both -S and -C-S supplies. ... 0.10, 0.11. Even some that were 0.0X. We thought it was an equipment error, so we checked with 3 other testers: same.
I think that's a bit misleading. The specifications of Type B, C and D MCBs require that they trip at 3-5, 5-10 and 10-20 times their In, respectively. That's different from "3-5, 5-10 and 10-20 times their 'thermal tripping current' " (whatever you mean by 'thermal tripping current') - since the specification also requires that they do NOT trip thermally at currents <1.15 x In.Although line - neutral could be measured in impedance Ω, it is normal to quote as prospective short circuit current A, and a B = 3 to 5 times thermal tripping current, C = 5 to 10 times thermal tripping current and D = 10 to 20 times thermal tripping current.
I'm not sure exactly what you mean by a "reduced low voltage transformer" (230V->110V, perhaps?) - but the 'inrush situation' would obviously have to 'look' pretty close to a ('zero impedance') 'short circuit' for the R1_Rn, even at the furthest point of a ring/radial circuit, to have appreciable impact on the inrush current.I have found some makes of reduced low voltage transformers do have a high in rush, with the same MCB plugged in close to consumer unit they will trip supply, but at centre of ring final or end of radial they will hold, the resistance of the supply cable is enough to reduce inrush current.
100 metres is, of course, quite a long cable by domestic installation standards but, even so, I remain a bit surprised - since, as I said, what you report implies that the (step-down to 110V) transformer must have bee presenting something approaching a 'sort circuit' to the supply at switch on. I would have thought that even the resistance of the tranny's primary would have avoided such a situation.Yes talking about 110 volt .... we had some old ones when working for GEC large steam turbines and at first I thought they were faulty, within a few meters of the 11kv to 400 volt transformer they would trip the MCB, but with 100 meters of cable they did not trip. Even close try a few times and you would likely hit the null point and they would work.
Of course, and that was really my point - that, although resistance is (presumably) a very small component of the impedance, if the situation is such that a difference in R1+Rn at different points in the circuit is able to produce appreciable difference in current (at start-up), that implies that the total effective impedance of the load during start-up would have to be lower than I would expect even the resistive component of the load to be.But what would its resistance be? I would expect most of the impedance of a transformer to be reactance.
I'm not sure that it is any 'yellow lump' or, rather, just the ones that eric encountered.Somebody must have a yellow lump handy which they could measure. Mine's in the garage, and CBA is an apposite term.
Sure, and I might even be tempted - but incandescents are essentially history. What very few I still have are ones in such rarely-used parts of the house that i haven't yet got around to changing them!
Well, for me, CFLs are almost 'history', but I certainly don't recall any have tripped MCBs - probably because their mode of death is very rarely "going bang" in the fashion that incandescents do. I've had mainly LEDs for a few years (a few CFLs left) and, whilst they do die occasionally, I'm pretty sure than none has ever tripped a B6 - most, even the cheapest ones, seem to have pretty trigger-happy 'fusible links' in them, which seem to blow before an MCB trips in the case of an 'over-current death'.