Borderline Fan Pressure. Clean Heat Exchanger?
1 Aug 2018
Hi
I had my boiler serviced and was told the fan pressure was -4.9.
The manual says pressure "must be greater than -4.9. Pressures below indicate that the heat exchanger will require cleaning".
The engineer said it will be fine until next year when it is recommended I have a strip down service. Is this sound advice or does it actually require cleaning? I have a feeling it was cleaned last year by BG but cannot be 100% sure.
Many thanks
Yes borderline I would of suggested the same, providing all other checks were ok
Cheers. Any advantages or disadvantages to cleaning at this reading? Other tests were passes apparently.
High Comb:
CO/Co2 ratio:0.0005
CO (ppm): 48
CO2%: 9.4
Low Comb
CO/Co2 ratio - 0.0000
CO (ppm) - 3
CO2% 8.7
Tightness test - Not done.
flue, combustion, burner ratio, ventilation all passed.
Operating pressure 18.57 mbar
Heat input 29.73 kW
Those readings are fine low is out by 0.1 but literally nothing to worry about , a full strip and clean of main heat exchanger will prolong the life and efficiency of the boiler and if it hasn’t been done before I would highly recommend that it is done as the burner seal is probably the original , also if the electrodes haven’t been replaced and you still have the original sight glass type I also would recommend they get replaced with the upgraded type.... was the kw rating also noted on the certificate ?
Electrodes have been changed. Not too sure about the seal.
Heat input 29.73 kW?
Have a feeling it was strip cleaned last year.
They said on the summary sheet I had no approved CO alarms but I pointed them out to them at the start ...
Kw rating is within , depends on what was done on the strip clean , there is one way they could of just taken off an inspection hatch and semi cleaned the main hex but there is no way that I can really tell from here lol . Maybe the service engineer added notes on the service sheet from last year what was done ?