Borderline Fan Pressure. Clean Heat Exchanger?

Discussion in 'Plumbing and Central Heating' started by Radam87, 9 Jan 2020.

  1. Radam87

    Radam87

    Joined:
    1 Aug 2018
    Messages:
    137
    Thanks Received:
    2
    Country:
    United Kingdom
    Hi

    I had my boiler serviced and was told the fan pressure was -4.9.

    The manual says pressure "must be greater than -4.9. Pressures below indicate that the heat exchanger will require cleaning".

    The engineer said it will be fine until next year when it is recommended I have a strip down service. Is this sound advice or does it actually require cleaning? I have a feeling it was cleaned last year by BG but cannot be 100% sure.

    Many thanks
     
  2. Sponsored Links
  3. Stadan20

    Stadan20

    Joined:
    21 Sep 2015
    Messages:
    3,295
    Thanks Received:
    780
    Location:
    Wiltshire
    Country:
    United Kingdom
    Assuming this is a Worcester. Model would be helpful
     
  4. Radam87

    Radam87

    Joined:
    1 Aug 2018
    Messages:
    137
    Thanks Received:
    2
    Country:
    United Kingdom
    Yes Worcester. 532.
     
  5. Stadan20

    Stadan20

    Joined:
    21 Sep 2015
    Messages:
    3,295
    Thanks Received:
    780
    Location:
    Wiltshire
    Country:
    United Kingdom
    And the model ......?
     
  6. Radam87

    Radam87

    Joined:
    1 Aug 2018
    Messages:
    137
    Thanks Received:
    2
    Country:
    United Kingdom
    532.
     
  7. Sponsored Links
  8. Stadan20

    Stadan20

    Joined:
    21 Sep 2015
    Messages:
    3,295
    Thanks Received:
    780
    Location:
    Wiltshire
    Country:
    United Kingdom
    Yes borderline I would of suggested the same, providing all other checks were ok
     
    • Thanks Thanks x 2
  9. Radam87

    Radam87

    Joined:
    1 Aug 2018
    Messages:
    137
    Thanks Received:
    2
    Country:
    United Kingdom
    Cheers. Any advantages or disadvantages to cleaning at this reading? Other tests were passes apparently.

    High Comb:
    CO/Co2 ratio:0.0005
    CO (ppm): 48
    CO2%: 9.4

    Low Comb
    CO/Co2 ratio - 0.0000
    CO (ppm) - 3
    CO2% 8.7

    Tightness test - Not done.
    flue, combustion, burner ratio, ventilation all passed.
    Operating pressure 18.57 mbar
    Heat input 29.73 kW
     
  10. Stadan20

    Stadan20

    Joined:
    21 Sep 2015
    Messages:
    3,295
    Thanks Received:
    780
    Location:
    Wiltshire
    Country:
    United Kingdom
    Those readings are fine low is out by 0.1 but literally nothing to worry about , a full strip and clean of main heat exchanger will prolong the life and efficiency of the boiler and if it hasn’t been done before I would highly recommend that it is done as the burner seal is probably the original , also if the electrodes haven’t been replaced and you still have the original sight glass type I also would recommend they get replaced with the upgraded type.... was the kw rating also noted on the certificate ?
     
    • Thanks Thanks x 2
  11. Radam87

    Radam87

    Joined:
    1 Aug 2018
    Messages:
    137
    Thanks Received:
    2
    Country:
    United Kingdom
    Electrodes have been changed. Not too sure about the seal.
    Heat input 29.73 kW?
    Have a feeling it was strip cleaned last year.

    They said on the summary sheet I had no approved CO alarms but I pointed them out to them at the start ...
     
  12. Stadan20

    Stadan20

    Joined:
    21 Sep 2015
    Messages:
    3,295
    Thanks Received:
    780
    Location:
    Wiltshire
    Country:
    United Kingdom
    Kw rating is within , depends on what was done on the strip clean , there is one way they could of just taken off an inspection hatch and semi cleaned the main hex but there is no way that I can really tell from here lol . Maybe the service engineer added notes on the service sheet from last year what was done ?
     
    • Like Like x 1
  13. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Loading...

Share This Page