Writing my recent reply to eric has made me wonder, specifically about C3s ....An EICR is carried out to the most recent edition of BS 7671. It is entirely irrelevant to what ever previous standard the installation may or may not have complied with. ... If you find a plastic consumer unit or red and black wiring then it doesn’t comply with the current edition of BS 7671 and needs to be noted on the EICR.
The introduction to BS7671 says ...
BS7671 itself does not actually seem to say anything about the 'coding' of non-compliances on an EICR, but refers one to the ("Informative, for guidance") Appendix 6, and the only reference to coding there seems to be in the specimen EICR form.BS7671:2018 said:Existing installations that have been installed in accordance with earlier editions of the Regulations may not comply with this edition in every respect. This does not necessarily mean that they are unsafe for continued use or require upgrading.
As you know, that form says that C3 means "Improvement recommended". If something was compliant with regs when installed, but not with current regs then IF (as the above quote acknowledges may be the case) the expert judgement of the person undertaking the inspection is that 'upgrading' is not required, then is it appropriate to give a code which means "Improvement recommended"?
Indeed, if an electrician whose expert opinion is that something does not require upgrading 'recommends that it should be improved', then I imagine that at least some people would suspect that this represented 'touting for unnecessary business'. It's even conceivable that Trading Standards might be unhappy with a qualified electrician 'recommending' work that, in their expert judgement, was not necessary/required.
In fact, I wonder if those undertaking EICRs even really think about this when coding things as C3. You say that, for example, red and black wiring should be "noted" on an EICR. If you mean that you would give it a C3 code, would you really be intending to 'recommend' a total re-wire?