I did not feel it was fair to talk about the problem in the thread where it started, the instructions seemed to ask for a type F RCD, but with a Domestic CU there is a problem with type F and B RCD's.
The problem is not done as a RCBO, type F two pole hard to get over 63 amp, type B two pole hard to get over 40 amp, type B often 4 module wide, and the price type F often over £150 and type B getting to £400 range.
It seems one can avoid the need for a type B by using a 6 mA DC detection unit to auto disconnect the supply, but only found them in electric car charging pods.
It seems not using type B can cause the RCD not to trip, but not using type F can cause it to trip when there is no earth leakage.
Not sure which is the worst? If a device needing a type B is fed from a type A as long as only that device and a TN supply even if it does not trip, is that really a big problem, only with a TT supply do we really rely on the RCD.
But type F is another question, clearly if high frequency causes a type A to trip, then no real away around the problem, or is there? Will a SPD help?
But if the electrician fits a type A then it keeps tripping he will be expected to correct the problem maybe free of charge, but to simply swap to type F in the consumer unit dropping to 63 amp with some manufacturers, some down to 40 amp, so it will likely involve a second consumer unit just for the item needing the type F RCD.
I personally feel disconnection devices and filters should be fitted to domestic appliances so nothing over type A is required. However This installation instruction set says
This raises two questions, 1) Can it share a RCD? 2) Will it need a type F RCD?
I would say it should not share a RCD and it does need type F, with a house with all RCBO CU it would need a separate enclosure, and likely also where just two RCD's again likely need a separate enclosure, with a high integrity consumer unit then maybe all the supplies from one RCD can be moved to RCBO's and that RCD changed to type F and a dedicated MCB.
However it seems to comply installation cost will be high.
So should any domestic appliance ask for better than a type AC or type A RCD?
Make sure to use a dedicated power circuit. NEVER use a power supply shared by another appliance
When installing the earth leakage protector, make sure it is compatible with the inverter (resistant to high frequency electric noise) to avoid unnecessary opening of the earth leakage protector.