Eh?
Not in what I read..
Eh?
Yes, I realised that's what you meant, but (sorry!) it doesn't alter the fact that I am a bit lostNot in what I read..
... If measurements gradually change and then 'settle down', despite your not 'touching anything', that can be due to capacitance/.capacitors associated with whatever is being measured.
What 'also' were you saying that I hadn't?Also true if there are capacitors in circuit, charging up and/or long cables, when measuring high resistance values/insulation.
Yes, I realised that's what you meant, but (sorry!) it doesn't alter the fact that I am a bit lost...
Not at all - I was merely wondering whether you had perhaps thought of (but forgotten to mention) an 'also' which I had overlooked, given that the only bit of my post which you quoted (when you wrote "also ... capacitance") was that relating to capacitance! In any event, I hadn't noticed that your comment related to measurements of high resistance, so we are 'quits' in terms of not have read carefully/fully enoughFact is I speed read and had not spotted your mention of capacitance. Is it really such a big issue if we both mention it?
I was wondering if moving the commutator could be inducing some kind of interference.
I may remove it from the housing and see if it reduces the variance.
Just to point out, I was not looking for accurate measurements per say. I was following a fault finding guide.
The guide suggested that while the values did not matter in themselves, a damaged bar would show an inconsistent result compared to the general value the others gave.
I was confused as I was seemingly getting wildly different values all the time.
I can actually see which bar is damaged, so I was more trying to see how that may manifest itself in a reading.
Unfortunately a bad connection while zeroing out the leads can very much result in under-reported readings during the real test.The saving grace is that, provided it is correctly calibrated, what none of these meters can do is produce a reading which is less than the true resistance,
That's very true, and I suppose that I was thinking of 'zeroing' as part of "correctly calibrated".Unfortunately a bad connection while zeroing out the leads can very much result in under-reported readings during the real test.The saving grace is that, provided it is correctly calibrated, what none of these meters can do is produce a reading which is less than the true resistance...
I've certainly seen a zeroing facility on a bench multimeter, not sure if any handhelds offer it.
My analogue ones do![]()
So do mine, in a sense, but it's certainly not intended as a means for compensating for test lead resistance when measuring small resistances. Since it's just a mechanical adjustment of the pointer, I imaginee that if one tried to use it to compensate for lead resistance, that would go wrong because of the non-linearity of the scale, wouldn't it (even if one had an analogue meter that could sensibly measure very low resistances)?My analogue ones do![]()
That would not really address the issue being discussed here, would it? No matter what equipment or methodology one uses to measure a small resistance, the accuracy of the reading will be at the mercy of the quality (resistance) of the connections between the measuring equipment and whatever is being measured.An accurate ( but inconvenient way to measure resistance is the Wheatstone bridge method.
Not for a 4-wire measurement.That would not really address the issue being discussed here, would it? No matter what equipment or methodology one uses to measure a small resistance, the accuracy of the reading will be at the mercy of the quality (resistance) of the connections between the measuring equipment and whatever is being measured.