Jonathan, here's a little calc for you, how long would it take to increase the flow temperature by 5C assuming rads demand of 3kw, boiler output 23kw and a flowrate of 21LPM.I see what you mean.
As seems to be the growing theme, there's no obvious option to do that on the Ideal's. Unless I need to open it up and flick some kind of switch somewhere... at which point I need a GasSafe engineer as the front panel is head-to-toe room seal.Thats the key to the whole thing, get the temperature down, you cant get a anti cycle time increase which will/would certainly do the trick, but if you can increase that pump speed, do.
I'm going to say 19 seconds.Jonathan, here's a little calc for you, how long would it take to increase the flow temperature by 5C assuming rads demand of 3kw, boiler output 23kw and a flowrate of 21LPM.
How long did it take the boiler temperature to fall by 10C when burner stopped firing?As seems to be the growing theme, there's no obvious option to do that on the Ideal's. Unless I need to open it up and flick some kind of switch somewhere... at which point I need a GasSafe engineer as the front panel is head-to-toe room seal.
If yours is an earlier version it might have a smaller LCD display.I think this is the right manual:
I'm finding it difficult but the way I'm thinking is that if I assume say that a total of say 60 litres (circulating system contents) has to be increased by 5C, then 20kw net will achieve this in 63secs and so on??.I'm going to say 19 seconds.
I'm thinking about it. Isn't it just heating the amount that's passing through the heat exchanger in the moment, rather than whole circuit. I also find it difficult.I'm finding it difficult but the way I'm thinking is that if I assume say that a total of say 60 litres (circulating system contents) has to be increased by 5C, then 20kw net will achieve this in 63secs and so on??.
Yes, I've always used .... dT = BoilerkwX860/60/LPM. so, 23X860/60/21, 15.7C, if the boiler return temp is 34.3C, then the flow temperature is 50C for a very very short time since the heat demand is only say 3kw, but the boiler return must reach 20.7C before the flow temp reaches 55C and burner trip so should one then consider the circulated rad contents as a "tank" that must be heated by 5C??.I'm thinking about it. Isn't it just heating the amount that's passing through the heat exchanger in the moment, rather than whole circuit. I also find it difficult.
EDIT: otherwise I can't see how it would go up 10C in 20 seconds, like in the case we are discussing.
I've had to think really hard about this.I'm finding it difficult but the way I'm thinking is that if I assume say that a total of say 60 litres (circulating system contents) has to be increased by 5C, then 20kw net will achieve this in 63secs and so on??.
Rather than a "tank", I've been thinking of it like an instant water heater. You only need to consider the amount of water that's actually flowed through the heater, and see how much that has been raised.Yes, I've always used .... dT = BoilerkwX860/60/LPM. so, 23X860/60/21, 15.7C, if the boiler return temp is 34.3C, then the flow temperature is 50C for a very very short time since the heat demand is only say 3kw, but the boiler return must reach 20.7C before the flow temp reaches 55C and burner trip so should one then consider the circulated rad contents as a "tank" that must be heated by 5C??.
I think the reason that its flying up in 10 secs or whatever is that the flowrate is very low, this happens regularly if TRVs are used, and even if the pump speed was at 100% then the (if) TRVs would still only allow the exact same flow circulation by throttling down?. No real problem for oil fired boilers as their 20/25 Litre Hx acts as a mini heat store.
Interesting, one way or the other, a gas boiler is certainly a instant heater since its contents may only be 2 litres or so, at 21lpm, 2 litres will have passed through it in less than 6 secs, the Hx metal will take some finite time to heat up however little but once this has heated up then in less than another 6 secs, the 23kw will be transferring to the water and the burner will almost trip instantly (from water at 45C) but not so from water at 34.3C, this must rise by another 5C to reach 39.3C, with a boiler dT of 15.7C = 55C, burner trip.