Hi all. I've been reading up on my heating system to try and optimise it. It was bought from the builders in 2007 and I don't think they did any kind of setup or tuning of the system. It's an S-plan system with an Ideal Icos HE-12, in a three storey well insulated house in a mild part of the country. I've had a look at turning the flow temperature down.
According to the manual the flow temperature can be between 30 and 70C. The boiler modulates, but not very much - the minimum is 9kW and the max 12kW, so I'd expect the boiler to cycle a bit once the set temperature has been reached. Aside from wether or not this is desirable, it doesn't actually behave this way. I've attached thermocouples to the output and return pipes just after they leave the boiler so I can monitor them. The CH is off now so I'm looking at how it works with the HW and here's the problem:
When I have the flow temperature set fairly cool, so it should be about 50C or so (yes I know this would be too low) the flow temperature still climbs up to 62C or so before the burner shuts off and the pump continues to run. Ok, fine, but then the burner doesn't come back on for ages, like 20 minutes, at which point the temperature has dropped to 42C or so which must be the temperature at the bottom of the tank. It just keeps pumping water around cooling the tank down. If I turn the flow temperature up higher, the flow temp goes up to 70C or so and then it still shuts off for ages and the temp drops back down to mid 40s.
I can't figure out how the boiler is responding to what the flow temperature should be. I thought maybe a faulty flow control thermistor but I've replaced that and it's the same.