New Cooker and hob set up help
2 Nov 2022
As part of a complete revamp of my kitchen
I’m having an integrated electric oven and induction hob fitted.
I have laid a 10mm cable from behind the new kitchen location into the ceiling and up, over and down to the fuse box.
Could someone please tell me the correct way to connect these two appliances to the 10mm cable and if this work or part of should be done before the kitchen units are installed.
I have a 45amp 2 gang dp cooker switch with a socket on & a 45amp unswitched cooker outlet plate if they’re of any use in these jobs.
Oven
16A amperage
Total load rating 3.2kW
Hob
220-240 voltage
Hope this is the right info - taken from the product specifications.
It’s a new circuit, so the work is notifiable. You need a registered electrician to do this. They should have done the design , installation and test themselves. Most won’t or aren’t willing to notify work done by others.
He/she will need to inspect the cable route so don’t cover anything over.
All new circuits must be RCD protected- you said “fuse box”. Fuse boxes usually don’t have RCDs, so there may be other work to do.
You can have an isolation switch, if you want. It’s not a regulation.
You’ll need a dual appliance connector plate.
What is the KW rating of the hob?
Hi Taylor
Thanks for your reply.
I’ve attached photos of the ‘fuse box’ and the hob.
Hope this answers your questions.
Your hob is 7.4kW, so a 10mm² cable with a suitable MCB will be able to handle the load.
You dont have a fuse box. You have a consumer unit.
I can see two spare positions in the photo but they are not RCD-protected slots, so you cannot use either of those, unless an RCBO is installed..
It looks like the other ways are RCD-protected so maybe you have a spare position that your electrician can utilise. You'll have to ask him/her.
I am concerned that (except for the downstairs light) all circuits are relying on one RCD, this is a bad situation as an earth fault on any circuit will cut the supply to the whole house. Again, your electrician may be able to re-configure the consumer unit.
It is, however, no longer compliant as it is not made of a fire-resistant material. MK is not longer making consumer units although parts are still available through another maker.
Hi Taylor,
Thanks again for your reply.
Happy to know the 10mm cable is suitable and can go ahead and lay the carpets. Upstairs
Would it help to know that both 6”shower” and 9 “cooker” are no longer be used.
Both the electric shower and Cooker have been removed?
Would one of these slots work?
I will have the electrician asses if the unit can be reconfigured as you suggest. Thanks!
One of those would be suitable.
Remember that I advised you:
That means that you cannot yet
The electrician will have to certify that they designed, installed and tested the new circuit (if you can persuade them to lie) so they will need to assess their risk of being sued if a fire develops from your cable routing.
Find your registered electrician here: https://www.electricalcompetentperson.co.uk/
I've got a bit lost here.
You say you have:
32A MCB in the consumer unit.
10mm² cable in place.
45A cooker switch... is this still fitted and wired in a suitable place?