I may be wrong, but I think that 6.6 kVA per house is well above what they consider to be adequate.I am working on a site, 5 new build domestic 3 bed house, dno is only supplying 2 phase supply (33kva max load) is this enough for connecting 5 properties?
Yes I think you are correct initially.I may be wrong, but I think that 6.6 kVA per house is well above what they consider to be adequate
No.We can expect each home to have occupants arriving home around same time so all heat pumps working together.
Could be. What does the design specification for the development say?(33kva max load) is this enough for connecting 5 properties?
Agreed.Yes I think you are correct initially. However I think that is intended originally as say 2 or 3kw per home for a more substantial number of homes, meaning less chance of greater variation of probabilities into the higher side of the graph.
Again, agreed.With the number of possible EV chargers as the "new kids on the block" we surely must consider their effect too as Murdochat mentions.
So 2 to 3 times of what we had not so long ago might not be actually that high at all when you filter in both of those reasons.
I also wondered that. However, on reflection, it occurred to me that if the plan is to do the usual thing had supply just one of the phases to each house, in turn, then three phases for just 5 houses might perhaps have been regarded as unnecessarily 'OTT'?I wonder if somewhere along the line a typo has occurred and it should be 3 phase. It would be a little unusual to run just 2. Far from unknown of course.
I wondered that too but I find it quite hard to believe it's cost effective to bury a cable containing 3 conductors when 2 or 4 are very standard and 3 is likely to not be a stock item. Then hooking 3 of a 4 core cable into 2 of the 3 phases is... well to be frank it doesn't add up.I also wondered that. However, on reflection, it occurred to me that if the plan is to do the usual thing had supply just one of the phases to each house, in turn, then three phases for just 5 houses might perhaps have been regarded as unnecessarily 'OTT'?
If, as one presumes,they are just going to supply one phase to each of the five properties, this discussion is really only of theoretical (or even 'terminological') interest, since it doesn't really matter whether the supply cable carries 2 or 3 phases. If (as, like you, I suspect is the case) it is actually a 3-phase supply, one of the phases would only be supplying one property.I wondered that too but I find it quite hard to believe it's cost effective to bury a cable containing 3 conductors when 2 or 4 are very standard and 3 is likely to not be a stock item. Then hooking 3 of a 4 core cable into 2 of the 3 phases is... well to be frank it doesn't add up.
Transitionally, DNOs rely extremely hevily on 'diversity' (across timeeee and properties). With just a shower and a large cooker, peak instantaneous loads in an individual property can easily exceed 80A,perhaps exceed 100A, but the average ('after-diversity') figure they work with has only been 2 - 3 kW per property....... I measured the 6 week lights period one winter our peak power was close to 25KW (I suspect we are on a 60A fuse as we're a looped supply) but I had no idea how many times or what duration, our average was below 1KW. Another way of looking at that is we were peaking at 80% of the total supply for 5 properties.
This may all very well be the case but the supply does need to cope with the peaks. If my understanding is correct the DNO only permits fusing to be twice the supply capacity so 16KW ~64A maximum fuse = 64*2/3 = 43A. So getting home from work, putting the car on charge, putting a load in the washing machine and starting to cook dinner ~60A or to put it another way 50% overload of the fuse and all of the allowance for all 3 properties. It smacks of a mistake to me.If, as one presumes,they are just going to supply one phase to each of the five properties, this discussion is really only of theoretical (or even 'terminological') interest, since it doesn't really matter whether the supply cable carries 2 or 3 phases. If (as, like you, I suspect is the case) it is actually a 3-phase supply, one of the phases would only be supplying one property.
As raised above, the question is whether the appearance of EV charging (and,to some extent, heat pumps) has totally moved the goalposts of that traditional approach - since,uniquely, EV charging can represent a large load which persists for long periods of time, hence potentially having a major impact on the average ('after diversity') demand.
Kind Regard's, John