I assume that a main RCD tripping while working on an isolated (at the breaker) circuit, means neutral to earth current. Is it a sign of a fault somewhere else?
Just wondering why there's any current able to flow. (Not sure what the earthing arrangment was)No fault, as such - other than the one you introduce when you touch Neutral and Earth together.
@richardindorset while the other circuits will still be live and when you touch the neutral and earth conductors it gives the current returning on the neutral an alternative path (the earth conductor) meaning that slightly less current will return through the neutral causing an imbalance hence tripping the RCD.All the neutrals are connected together on the RCD circuits and all the earths are connected together in your installation
OK. Will the type of earthing used will have a bearing on this?@richardindorset while the other circuits will still be live and when you touch the neutral and earth conductors it gives the current returning on the neutral an alternative path (the earth conductor) meaning that slightly less current will return through the neutral causing an imbalance hence tripping the RCD.
the higher the load the higher probability of the rcd tripping.
Bear in mind, If there is already a neutral to earth fault in any circuit circuit when shorting N and E, the current that should flow to the outgoing neutral, though the coil in the rcd can flow instead along the final circuit neutral through the fault and to earth bypassing the coil in the RCD. If the relative resistances of the two possible paths are right there then may not be enough current to trip the RCD...OK. Will the type of earthing used will have a bearing on this?
www.diynot.com
Thanks! So a parallel path is created for the neutral current thus creating the inbalance in the coil and tripping the RCD.
Yes, as with TN-C-S the link between earth and neutral is closer to the head as with TN-S and with TT the voltage could easily be in the 10s of volts between neutral and earth.OK. Will the type of earthing used will have a bearing on this?
I assumed the impedance of the earthing system would have an effect on this. Interesting fault condition to have. I wish I'd measured the voltage between earth and neutral at the socket I was working on now.Yes, as with TN-C-S the link between earth and neutral is closer to the head as with TN-S and with TT the voltage could easily be in the 10s of volts between neutral and earth.
This is why you find a fault on a toaster can trip the RCD when the kettle is used, the higher the load, the higher the voltage difference between earth and neutral.