Ah ok yes, it does because it is entering the house - not because it is going to the boiler.I thought that the gas pipework has to be bonded has it enters the house ,
This arrangement does not comply and never has.
Oh my goodness.
each building has to be treated as a zone in it's own right, therefore:
In the garage there is a MET bonded to the CU and extraneous metalwork
In the house there is a MET bonded to the CU and extraneous metalwork
The fact that the garage feeds gas to the house is irrelevant
The fact that the house feeds electricity to the garage is irrelevant
My interpretation of the various documents (and I don't claim to know every single detail) is:View attachment 381880
In the garage I have shown 2 wires in green to the gas pipes and alternatively one wire in purple to both pipes as long as it is in one piece, this can be achieved by not cutting it or some other means of making the join between the 2 wires permanent ie by putting both wires into a single crimped connector or soldering/sweating.
Also it is permissable to use the CU earth bar as the MET if there are sufficient adequately sized terminations.
The earth from house to garage should be 10mm² due to the gas bonding. Ideally without a joint but not a necessity.
Your attachment is what I am doing !This arrangement does not comply and never has.
There are differences between documents on this point,they all say as it enters the house but some duplicate the requirement at the meter, ie within 600mm and before the first tee, others sayThe only thing in question now, is where to fit the 10mm bonding to the gas pipe in the house, I can't fit a bond to the gas pipe has it enters the house, it comes in under the floor boards, so was asking now if bonding to the gas feed to the boiler will be ok !
So if the position at the boiler is the earliest practical position then so be itas near as practicable to the point of entry of that part into the
premises.
Yes it does have to be continuous, but it is to the MET in the same building, The link between the 2 METs is different rulesBut I thought that the 10mm bonding from the MET to the Meter had to be continuous, if I put in a earthing terminal before the meter it wil have broken the continuous run !
That is correct but if you are describing my sketches purple wire then yes a single wire as in the description or 2 seperate wires as in my sketches green wires.That is good then so will pull through a the 10mm from the MET to a earthing block in the garage, then 10mm to the CU, outlet pipe of gas meter, and the gas riser , job done !.
ps: The difficult part is attaching a bond to the riser, not sure how to go about doing that, would have to be some sort of heavy clamp that will dig into the steel pipework, just the normal SS steal straps wond do I suspect !
Am doing the 2 green wires, and tks for making it clear, it was getting a bit messyThere are differences between documents on this point,they all say as it enters the house but some duplicate the requirement at the meter, ie within 600mm and before the first tee, others say
You are welcome.Am doing the 2 green wires, and tks for making it clear, it was getting a bit messy![]()
No it doesn't.Yes it does have to be continuous,
As you presumably saw, I had that discussion with EFLI and, although I don't think either he or I are absolutely certain, as I see it ....Oh my goodness. .... each building has to be treated as a zone in it's own right, therefore:
My view is that if the house's earth is 'exported' to the garage, then there is only one true MET - that to which the DNO's earth (or,if TT, the earth rod) is connected. There might be things that resemble a "MET" in other places, which are electrically connected to the actual MET, but they lack the "M" and therefore aren't METs (any more than an earth terminal in a JB or accessory is).In the garage there is a MET bonded to the CU and extraneous metalwork
Since when, and why? I would be totally comfortable with that.This arrangement does not comply and never has.
As far as I am aware, BS 7671 has never said that bonding conductors must be 'continuous'. If I recall correctly, the myth arose because there was a day when the wretched OSG (but not BS7671) said this, but it's not even in the OSG now.No it doesn't.