Although it's probably a fairly reasonable 'nearly worst case' scenario, I think that "We" relates to some IET person you once heard speaking?We consider sockets on a 32 amp supply as having a design current of 26 amp, that is 20 amp centre of ring and 12 amp even spread ...
That's the approach the OSG takes. However, as I recently wrote, those 'maximum circuit lengths' result not only from consideration of voltage drop but to the suggested 'guidance' figures for maximum VD. I don't think many people are particularly concerned about these VD considerations and, in any event, the calculation of 'maximum theoretical VD' relate to a situation which will almost never arise - with the circuit loaded right up to it's capacity (e.g. 32A for a ring) and, even then, a VD in excess of the 'guidance' figure could only ever happen at the midpoint of the ring..... so for volt drop 26 amps is used, allowing up to 106 meters of 2.5 mm² cable to be used. .... But split that into two with 20 amp overload, and we then work on the full 20 amps, so again with 2.5 mm² cable, we can have 32 meters of cable.
As I recently wrote, if one considers Zs (much more important) rather than VD, then the maximum circuit lengths can be quite a lot greater than you or the OSG suggest
A circuit for which calculations indicate the the VD at the worst point (centre of ring or end of radial) could theoretically exceed the 'maximum' guidance figure will (provided Zs etc.is satisfactory) can be fully compliant with BS 7671, provided only that the voltage drop does not "impair the safe functioning of connected equipment)
"Increases" relative to what?This would show an increase of 0.59 Ω on the loop impedance reading. .... This would show an increase of 0.79 Ω on the loop impedance reading. ....
with an increase of 0.97 Ω on the loop impedance reading.