If you could rearrange the circuits to have separate upstairs and downstairs power rings, then have upstairs lighitng and downstairs power on RCD A and downstairs lighting and upstairs power on RCD B.
Ideally I would, I was surprised to find only one ring for all the sockets, I just havent yet worked out the routing of the RF
fair comment! though I know the integrity of this is sound, I installed it myselfPut the shed radial on an RCBO not off one of the RCBs.![]()
Cooker circuit is already there (6mm), its just been extended to the pantry for the fridge/freezer on 2.5mm and will be on a 16APut in a cooker circuit in case you/someone wants leccy cooking at a later date.
I'm not used to doing domestic works, so am just a bit jumpy about having everything on (albeit 2) RCD's, what with 3 fridges and a tumble dryer! I guess these things can be a bit leaky!
I'll split it up to get ballanced loading, see how it works out
Thanks for the advice
![]()
Nowt wrong with that, homeboy.
2.5mm on a 16A OPD is fine.