We've ordered an EV charger via Octopus and they came and did a site survey and we have a few problems that need addressing.
The house has a TT electrical system and the earthing rod resistance came back as 350 ohms and they want it lower than 200 ohms.
The second problem is the gas meter is not bonded.
The water and gas enter the property right next to the earthing rod. The property was extended about 20 years ago and the gas meter was moved to the new outside wall.
When they moved the gas meter they damaged the water pipe and when this was repaired I took photos which show the locations of the green plastic covered copper water pipe, the yellow gas pipe and the earthing rod. The cut off yellow pipe went to the old gas meter.
There are two 10mm earth cables that run from the consumer unit, one going to the earthing rod and the other attached to the water pipes by the stop tap just behind the wall shown above. Both cables had low resistance and look to be in good condition.
1. The yellow gas pipe looks to be plastic to me and if this is the case does the gas meter need to be bonded?
2. If the gas meter does need to be bonded does it have to have a separate earth cable to the consumer unit or could it be joined to the water pipes bonding as the services enter the property?
I ask this as the distance between them is about 500mm and both are accessible at the back of a cupboard so it would be easy to whereas to get an extra cable to the consumer unit would be lot of hassle as it's in the centre of the property quite a distance away and it's not an easy route.
3. To improve the grounding should the earthing rod be removed to check for corrosion, replaced with a larger diameter one (current one is 9mm) and adding an additional rod a couple of meters away and connecting the two together?
The other alternative option is to have the property converted to a PME system thus doing away with the earthing rod and if the gas meter needs earthing then we could reuse the existing earth cable that went to the earthing rod.
4. I've had a quote from the DNO for this and it's about £165 and would take about 6 weeks however other than switching the earths to the new earthing terminal is this likely to require a lot of extra work as the plastic consumer unit is 20 years and fitted to the regs back then. I can give more details of the consumer unit setup as and when needed.
We currently have a looped supply with next door and the DNO have given the go ahead for a restricted charger which will be unrestricted after the property is unlooped in the future but this is likely to be months away.
5. Does a looped supply cause any problems for converting to a PME system, is it allowed if your neighbour is on a TT system?
The DNO recommended waiting for unlooping before converting to a PME but obviously this delays things quite a bit.
Any thoughts on the above before I try and get a sparky involved so I know what I'm talking about?