No call for central heating - problem solving
8 Jul 2008
Derbyshire
System suddenly decided to stop calling for central heating.
Just wanted to go through my through process and get any other ideas where to check.
It's a very simple open vent non condensing set-up with an old dial thermostat and a basic central heating/hot water control switch.
1) Central heating suddenly did not come on when time to
2) Hot water calls fine, the gas valve opens fine and the boiler fires up for hot water.
The hot water is gravity circulated so no pump is triggered for that.
3) My initial suspicion lies with the hot water/central heating control. It was being a bit dicky recently. The buttons could be a bit temperamental, but if left alone it seemed fine.
Screenshot 2026-04-07 at 17-43-08 drayton-29206bq-programmer~5016254200481_03c (WEBP Image 600...png
4) Then I checked the thermostat and rotated it and realised there was no clicking at all, so then my attention turned to that.
This is the first time I noticed anything amiss with it, as it was so inaccurate, it was more or less defunct, and permanently called for heat. But it did click if you rotated it enough.
Inside the thermostat it seems to be permanently making contact with the lower connection, no matter how the dial is turned.
Screenshot 2026-04-07 at 17-47-41 (JPEG Image 2048 × 1536 pixels) – Scaled (56%).pngScreenshot 2026-04-07 at 17-48-30 (JPEG Image 2048 × 1536 pixels) – Scaled (56%).png
Edit: I have confirmed that while the thermostat is old, it is functioning fine, I tested it with a hairdryer and it moves to the top contact when warm enough, and drops when it has cooled back down.
So my suspicion is back centred on the control unit just not calling for the pump.
Or, if I end up excluding that, the pump?
Edit: I suppose I could bypass the control unit to call for heat and that would test that.
You seem to be most of the way there with fault finding. Yes you can bypass the CH part of the control unit to test, this is quick (and possibly the safest option as it doesn't rely on prodding live parts with a test meter.) Just link whatever is in the CH on terminal to live. You haven't shown what other parts are wired to the system, some systems rely on the hot water to be up to temperature before the heating can be allowed to operate.
There are a couple of ways to wire gravity hot water systems depending what valve is fitted for the cylinder, motorised or thermo mechanical or nothing. If you have a meter you can test if mains is appearing at the heating terminal of the timer when CH is on if this is accessible . You might be able to test it at the room stat if you test between live in and neutral (if present) or live in and earth. The terminals are under the plastic cover shown in your photo. Turn off the mains before opening the cover if you test at the room stat as there is a lot of dangerous exposed live parts in these.
With the heating timer on and the room thermostat calling there should be 240v measured across terminals 2 and 1 as well as 2 and 3. If that is good test for power at the pump.
The system has no cylinder valve, so the hot water is always on if the central heating is on.
So the stat pretty much goes to the pump via the timer/programmer, I think.
Screenshot 2026-04-07 at 23-39-53 (JPEG Image 2048 × 1536 pixels) – Scaled (56%).pngScreenshot 2026-04-07 at 23-40-08 (JPEG Image 2048 × 1536 pixels) – Scaled (56%).png
So based on the diagram on the back of the timer, I should just bridge L and number 4?
Could I also do some kind a continuity test on the programmer? Should I not get some kind of continuity from the L prong and CH prong if it is switch to 24hr or something. Although I would expect the unit needs to be energised to get any kind of continuity.
Maybe do some voltage testing? Heating on to room stat should be 240vac, room stat to motorised valve and or pump should be 240vac
Hmm, I bridged Live and the CH 4 terminal and nothing......
This set-up is as simple as it gets, i have no wiring centre for the central heating.
I am back to thinking the thermostat is the failure point. Even if it did not seem to fire in either position, something else must have failed on it.
link 1 and 3 at the stat next then. If the pump doesn't run then there is either a fault with the pump or the wiring somewhere between the controller and pump.
You need to beg, borrow, or steal some means of checking voltages, and to make use of it - otherwise you are fault-finding half-blind!
Yeh, I have have a multimeter.
I was just being lazy as everything seems to be getting power. But you are correct, I have not confirmed it.
So, just so I am clear as to what is going on here, is what I have marked up correct?
The "earth" is being used as a switched live.
So first check I am getting 240v coming in between 2 and 3?
Then check I am getting 240v between 1 and 2 when the thermostat is meant to be sending?
Ok, the initial results are not what I expected.
It looks like there is no power coming into the thermostat!
It seemed to be fluctuating quite a lot, and I did get a few readings at 240V but it mostly seems to be supplying less than one volt.
It then settled after a bit but still seems stable-ish at under 1V
So, cable issue....potentially?
Is it likely the thermostat has it's own fuse as nothing else has tripped in the house. And before you ask, it's a very old manual fuse box with limited information.
The only reliable way to measure a voltage, is against a known reference. That known reference will likely be a definite earth point. Your central heating pipe work ought to provide a good earth, as should an earth pin on any 13 amp socket.
The earth wire should never be used as a live conductor.
It seemed to be fluctuating quite a lot, and I did get a few readings at 240V but it mostly seems to be supplying less than a one volt.
If that is a modern high impedance digital meter, the problem is that they can pick up and display voltages which have no current behind them - they can show voltages just picked up from the air. Unless you see a good, solid mains voltage shown, assume there is no voltage, for test purposes.
Ok, I tested line and neutral with a known good earth (extension cable) and still 0v.
But.....and this is where I am intrigued....and potentially back to suspecting the pump.
I realised I was testing the thermostat without the timer/programmer energised. So i set CH/HW to on, and then tested the thermostat.
First with the thermostat calling for heat.
I got 240V at both 2 and 3 and 1 & 2
Then I heated the thermostat until it stopped calling for heat.
I got 0v at 2 & 3, but I still had 240v and 1 & 2.
So....thermostat seems to be working.....but....not the way round I thought? But it's still the correct way for this thermostat?
It's been wired like this for 50 years....so...it seems like it's still doing it's thing correctly.
So....back to the programmer and the pump? I'm again thinking it must be one of these two things.
The reason for showing the wiring centre, was that I have three diagrams, showing how the system has been added to over the years, adding a tank thermostat allowed one to run boiler for domestic hot water (DHW) in the summer, other than a simple timed run, ensuring it gets hot enough to stop legionaries, and the third with a motorised valve so in winter the DHW can be cooler than CH water.
I was always told cheaper getting DHW from the CH boiler to using an immersion heater, however when I was able to see how much the immersion used, I found that was not the case, so summer I use an immersion heater now.
I have found turning up pump speed sometimes works, but it is a temporary fix only, if it needs turning up, likely pump on its way out.
Furthermore, I also found with C Plan sometimes upper floor radiators heat up when they shouldn't, once water starts to circulate, turning off pump it often continues to circulate. So although when the central heating runs, it heats domestic hot water, I don't ever program DHW on its own, theory the TRV heads should turn off radiators, but if a set of batteries becomes discharged, the TRV defaults open, and I am not always catching when the non computer linked TRV head batteries get discharged.
The 240v, goes via the following sequence. Timer > stat > pump and boiler.
If you are seeing 240v out of the stat, that means timer and stat, are calling for heat, therefore your next check needs to be at the pump.
Another possibility, might be, that you have lost the neutral. Checking with your meter, at the pump, between L & N, when there is a call for heat, should help identify that.