Worked on a static caravan site for the first time today and not sure about some of the installation methods used. The TNCS supply to the outdoor joint boxes seems fine: 16.0mm SWA into the meter and henley block, then through a 80A mcb and a 30mA rcd. The things that I question are the cable from this joint box to the CU inside the home is 16.0mm T&E, thus making the main earth only 6.00mm. The set up inside is ok with 10.0mm eq.bond. but there is another 30mA rcd as the main switch for the CU.
In my mind, the CU 30mA rcd is correct inside, with perhaps a 150mA (delayed?) rcd in the outside joint box protecting the cable, if needed. As it is, there is no discrimnation between the two and they both trip alternately during the rcd tests. Also, the 16.0mm t&e should be 16.0 SWA, for both underground protection and a 16.0mm main earth. Or am I wrong to term this the main earth? Would that be just be the earth from the supply to the CU back at the point which feeds the whole site?
Cheers,
Ants
Cheers,
Ants