Boiler ignition keeps tripping circuit breaker
21 Jan 2008
Southampton
I have a Glowworm Energysaver 60e boiler which is about 8 years old. Every time the boiler "ignites" (not sure if this is the right terminology) it causes the RCD circuit breaker to trip.
If I reset the RCD, I can hear the boiler switching on. About 5 seconds later it goes to ignite and then the RCD trips immediately.
If anyone could provide some suggestions as to what may be causing this to happen and if it's possible to fix it myself I'd be most grateful.
You have to isolate things like the pump and other probably electricals. Need a fair understanding of what's connected and the sequence of operation, and ideally a sensitive AC clamp meter. It could be the earthing & connections around the ignition.
Thanks for your prompt reply Chris, I'll start isolating things as you suggest.
I had a very similar problem 3 months ago and it was the pump. I disconnected the wiring to the pump from the connector feed from central heating and wired in a seperate feed. This to took out the circuit breaker. The pump had failed.
The actual ignition spark causes a small current through the earth.
If there are other leaking appliances or wiring in the property then the combined current will often exceed the 30 mA trip current.
The boiler is then blamed when in reality its something else.
I went to one where it was the kettle but it only tripped when the boiler fired up.
The cure was to fit the boiler to a non RCD circuit! Thats always better practice anyway.
Tony
After isolating things and testing everything it is definitely the boiler.
I removed the outer cover to find quite a lot of water sitting in the bottom of the casing, and moisture on the electrics. It looks like the condenser is leaking, so I'm going to get a professional in to look at it.
Thanks for your help!