The CU's being released by MEM, Crabtree etc come in many varients, but the main line has a main switch with 3 or 4 non RCD Protected circuits, ideally suited for RCBO's for nuisance items like cookers etc. They can also be used for non RCD protected circuits (if any....hopefully the smokes).
There are then two individual 30mA banks of ways. Consencus is to ideally have two lighting circuits up and down each (4 total), and split these over the two RCD's. Similarly with the sockets. If you do fit only a single lighting circuit upstairs, you should make sure the sockets and lights upstairs are on different RCD's.
Also, with regards ring final circuits. The correction factor has changed, making it near impossible to use a 2.5mm ring if the cables are in an insulated wall or even loft. Looks like the end of the ring aint far away - it will be radials or non-standard circuits (4mm rings or even 20amp 2.5mm rings).