1.5mm spur to double socket

Discussion in 'Electrics UK' started by jonbey, 26 Aug 2020.

  1. jonbey

    jonbey

    Joined:
    17 May 2012
    Messages:
    5,325
    Thanks Received:
    291
    Country:
    United Kingdom
    I have what looks like a 1.5mm spur to double socket in a bedroom. Rest of electric cables are 2.5mm. If the cable is rated at 20 amp this should be OK, unless somebody uses a hair dryer and vacuum cleaner and something else in an extension lead, at the same time, on that socket? Or should I start removing floorboards and run a 2.5mm cable?
     
  2. Sponsored Links
  3. AndyPRK

    AndyPRK

    Joined:
    4 Jan 2009
    Messages:
    5,197
    Thanks Received:
    489
    Location:
    Herefordshire
    Country:
    United Kingdom
    Is it on a 32A MCB ?
     
  4. jonbey

    jonbey

    Joined:
    17 May 2012
    Messages:
    5,325
    Thanks Received:
    291
    Country:
    United Kingdom
    If that what the 32 here means, yes. Otherwise, no idea!

    unit.png
     
  5. EddieM

    EddieM

    Joined:
    15 Feb 2009
    Messages:
    9,676
    Thanks Received:
    582
    Country:
    United Kingdom
    I like the B20 ?
     
  6. Sponsored Links
  7. jonbey

    jonbey

    Joined:
    17 May 2012
    Messages:
    5,325
    Thanks Received:
    291
    Country:
    United Kingdom
    No idea what that circuit is! I turned all off then tested each to find out what it did, and that appears to be connected to nothing at all.
    But there might have been storage heaters in the house once, judging by the storage heater stones found in the garden...
     
  8. JohnW2

    JohnW2

    Joined:
    28 Jan 2011
    Messages:
    44,381
    Thanks Received:
    2,812
    Location:
    Buckinghamshire
    Country:
    United Kingdom
    Indeed
    Not really an issue, per se. If there's just one double socket, it doesn't make any difference how many things are plugged into that via extension leads, since the plug of an extension lead will, itself have only a 13A fuse in it.

    Kind Regards, John
     
    • Like Like x 1
  9. sparkwright

    sparkwright

    Joined:
    20 Aug 2009
    Messages:
    7,517
    Thanks Received:
    921
    Location:
    Dorset
    Country:
    United Kingdom
    Old immersion water heater circuit perhaps?
     
  10. jonbey

    jonbey

    Joined:
    17 May 2012
    Messages:
    5,325
    Thanks Received:
    291
    Country:
    United Kingdom
    Could be. There was something old in the old kitchen, now removed. No idea!
     