13 amp Socket off Shower switch
31 Dec 2005
Cheshire
The shower switch (outside bathroom) is fed by a 10mm cable and protected by a 32 amp cb. I want a 13 amp socket next to it, can I just fit one of those cooker and socket switches.
thanks
No not if its connected to your shower. Unlike a cooker which has a varying load a shower is more or less a constant load.I have seen a FCU spurred of a shower to supply an extractor fan, but thats a fixed and very small additional load.
What do you want to plug into the socket?
Regards,
DS
thanks
Are you sure about those sizes - 10mm cable and a 32A circuit breaker would be a very unusual choice, and is not suitable for the majority of modern showers.
As for the cooker switch/socket - if probably could depending on the shower rating.
However refer also to the picture below:
The socket will be used for a table lamp.
The shower is a 10.5kw and its definitely 10mm cable and the breaker says B32.
As has been implied, that's a problem. The 10mm² cable is fine for a 10.5 kW shower, but that shower will probably take about 43.75A (assuming it's 10,5kW at 240V), and that's far too much for a B32 (i.e. 32A) breaker - it should be a B45 or B50. You need to get that sorted out.
Kind Regards, John
Kind Regards, John
Ok will do, apart from that can I fit the switch (cooker + socket) for a table lamp.
Electric shower circuits should be left to electric shower only. Your best option would be to extend or spur off an existing socket circuit. There could also be a requirement to protect new cable/socket with 30mA RCD protection if the circuit being extended/spurred does not already have this protection.
And law would expect you to prove the work you are doing and completing is safe.