I'll start from the beginning. I got in the shower a week ago, and the water came on, but did not get hot. I noticed that the neon in the isolator came on, but when I turned on the shower, it went out. After opening up the shower, I found water coming out of the heater element can, so decided to get a new shower. I thought it must be shorting out inside with the leak, although the RCD and shower breaker in the fuse box did not go off.
I fitted the new shower today, and it also will not come on. The neon in the isolator switch goes out when I turn it on, as with the last one.
I measured 250V between live and ground, and I also have 150V between neutral and ground. I also have 28V between live and neutral. When I measure the voltage between neutral and ground, the power neon comes on on the shower.
I have 2 showers, so I swapped the circuit breakers over in the fuse box. I get the same happening, so I know it is not a faulty breaker, and the other shower works fine.
Has anyone any ideas what is going on? I have not changed any electrics for at least 6 months (swapped a dimmer in the lounge), so I don't see why something should have changed.
I fitted the new shower today, and it also will not come on. The neon in the isolator switch goes out when I turn it on, as with the last one.
I measured 250V between live and ground, and I also have 150V between neutral and ground. I also have 28V between live and neutral. When I measure the voltage between neutral and ground, the power neon comes on on the shower.
I have 2 showers, so I swapped the circuit breakers over in the fuse box. I get the same happening, so I know it is not a faulty breaker, and the other shower works fine.
Has anyone any ideas what is going on? I have not changed any electrics for at least 6 months (swapped a dimmer in the lounge), so I don't see why something should have changed.