I know the 15th is no longer applicable, but was intrigued by the wording of these regs*:
Installations which are part of a TN system
413-9 The protective devices shall be of one or more of the following types:
- overcurrent protective devices,
- residual current devices.
provided that where the neutral and the protective functions are combined in one conductor (PEN conductor) a residual current device shall not be used.
Installations which are part of a TT system
413-12 The protective devices shall be of one or more of the following types:
- residual current devices,
- overcurrent protective devices.
NOTE - Residual current devices are preferred.
413-9 Does that mean you cannot use an RCD on a PME supply?
413-12 No overcurrent devices on a TT supply?
* Yes, I'm a fad sucker who reads old regs in his spare time...