now that from july 1st most installations have to be on a 30mA RCD
do we need to RCD test circuits apart from sockets and showers etc.
i.e the things that have 5s disconnection times
 
All final circuits up to 32A on a TN system now have a reduced 0.4s disconnection time.
 
If you don't test the RCD, how will you know it is working within spec?
 
so basically every circuit domestically on TN
has a 0.4s disconnect time now then?
what about TT installs?
 
so basically every circuit domestically on TN
has a 0.4s disconnect time now then?
what about TT installs?

RTFB (Read The 'effing' Book)

If you don't know the regs how can you comply with them? And if you are doing this work for profit, not having a copy is practically criminal!
 
Garymo, chock on lad, Quote the Red Bible

Maximum disconnection times

120V <Uo =<230V TN 0.4 max TT 0.2 (a.c.)

230v < Uo =<400 TN 0.2 TT 0.07 (a.c.)

This leads to another question however

When regularly reading the supply voltage I get over 230v normally 249v ish

Now I was always told to use the readings YOU get, so does that mean the latter should really apply, or lets just all agree it is 230v and so the former applies :?:
 
When regularly reading the supply voltage I get over 230v normally 249v ish

Now I was always told to use the readings YOU get, so does that mean the latter should really apply, or lets just all agree it is 230v and so the former applies :?:

As GaryMo has indicated, this is the nominal line voltage to earth, Uo, so the times stated in table 41.1 apply.

There is nowhere on any BS 7671 form to record the actual voltage at consumers' supply terminals, so I'm not sure who has told you to use such readings and for what purpose.
 
Hi Dingbat, what was being suggested by the lectures at college was that although there is a nominal figure of 230v, we know that often we can find voltages in excess of this.

After all, they've really only changed the nominal voltage in number rather than supply thus far.

So the arguement is that when investigating faults / new installations etc that it may also prove beneficial, in some cases, to carryout calcs using the actual voltage to ascertain if this could be having any adverse effects.

Thats all
 
But you were asking about the application of the wiring regulations, in which only nominal voltages are used.
 
An example would be maximum earth fault loop impedance for a given protective device, lets say a BS60898 B6 MCB......

Using 230v: 230/(6x5) = 7.66ohms (6.13ohms 80% ROT)
Using 249v: 249/(6x5) = 8.3ohms (6.64ohms 80% ROT)

Basically, using 230v would be erring on the side of caution and what you should base your cable calculations on.
 

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back
Top