The discussion also seems to focus on the provision of RCD protection within these 'CUs' - people really must stop calling them Consumer Units - the French think we eat them if we call them that - the term used by the UK in Annex ZA of BS 60439-3 in 1994 was Customer Distribution Board (CDB) :D.
I suggest you take that up with the French and the IEE because until the definition in 7671 changes they are still Consumer Units. And why and earth would anyone want to complicate things and call them anything else?

It would appear then that we are only considering the application of 314 to a limited sub-set of electrical installations when, in fact, it applies to all electrical installations.
Apart from domestic installations, I can't think of any other installation configuration where a minor single circuit fault will knowingly trip other circuits and the fault free circuits can’t be reset.

Page 23 - 26 of the 17th OSG
Fig 3.1
• The four RCD protected circuits are un-maintainable without tripping the RCD which would affect the other three circuits. That does no meet 314.1 (ii)
• If the fault was on a non-lighting circuit but a lighting circuit was one of the four connected to the single RCD that does not meet 314.1.(iii)
• If an N-E fault developed on one of the four circuits it could not be isolated so the other three would be affected until the fault was cleared. Without knowing when the fault might occur and how long the repair would take nobody can claim to have met 314.1 (i).

Fig 3.2
• The four 30mA RCD protected circuits are un-maintainable without tripping the RCD which would affect the other three circuits. That does no meet 314.1 (ii)
• The four 100mA circuits are un-maintainable without tripping out the main 100mA which would affect all eight circuits. That does no meet 314.1 (ii)
• If the fault was on a non-lighting circuit but a lighting circuit was one of the four connected to the single RCD that does not meet 314.1.(iii)
• If an N-E fault developed on one of the four 30mA RCD circuits it could not be isolated so the other three would be affected until the fault was cleared.
• If an N-E fault developed on one of the four 100mA RCD circuits it could not be isolated so the other seven would be affected until the fault was cleared.
• Without knowing when the fault might occur and how long the repair would take nobody can claim to have met 314.1 (i).

Fig 3.3
• Meets all parts of 314 for TN installations.
• May meet all parts of 314 for TT installations as long as a 100mA TD RCD is not used as an incomer. However, Merlin Gerin don't agree and their RCBO's can't be used on TT installations.

Fig 3.4
• The two sets of four 30mA RCD protected circuits are un-maintainable without tripping the RCD’s which would affect the other three circuits. That does no meet 314.1 (ii)
• If the fault was on a non-lighting circuit but a lighting circuit was one of the four connected to either of the RCD’s that wouldn’t meet 314.1.(iii)
• If an N-E fault developed on one of the four 30mA RCD circuits it could not be isolated. So the other three would be affected until the fault was cleared.
• If an N-E fault developed on one of the four 100mA RCD circuits it could not be isolated. So the other three would be affected until the fault was cleared.
• Without knowing when the fault might occur and how long the repair would take nobody can claim to have met 314.1 (i).

Fig 3.5
• The same as 3.4

So IMHO, for TN installations, the only satisfactory solution is Fig 3.3 and for domestic TT installations...who knows

Edit...changed my mind
 
Sponsored Links
I think this thread has been 'done to death' so I don't want to keep it running.

However, if you want to discuss section 314 start another thread.

BTW the OSG is limited to 100A installations and is, IMO, of limited use - for that reason I don't own a copy so it would be no good referring to it.

My comments on the Customer Distribution Board are, in fact, true - however, I included them as a joke - hence the smiley.
 
However, if you want to discuss section 314 start another thread.
No thanks! :LOL:

BTW the OSG is limited to 100A installations and is, IMO, of limited use - for that reason I don't own a copy so it would be no good referring to it.
I agree that all guides are of limited use but the OSG is the domestic sparks bible. So if one wants to comment and question domestic installation methods and practices one really needs to own a copy.
 

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Sponsored Links
Back
Top