I don't know; you brought up the subject.By who?
Ok. Previous reply applies then.This is not possible it is a required part of the system.
It cannot be avoided sometimes. What was the term you think technical?Purposly said I would not use technical terminology to avoid clouding the issue.
I do not know what the main zone is.Is the main zone not intended to be from the moment you enter the front door of the property?
Yes, more or less. Apart from the main bonding to incoming services, all other bonding is supplementary - supplementary(in addition) to the main bonding.Supplementry, again correct me, is to ensure that a particular area that is of higher risk e.g. bathroom, within the property, is at a consistant voltage level so eliminating the risk of shock?
And you called my spoon analogy poor. Fit two flexes if you want.Scenario - gas boiler develops earth fault and earth wire in flex has failed boiler casing becomes live and, if water and gas pipes not connected together, they also become live. Is that a safe situation? Touch outside tap or the pipe I previously described and it could be curtains.
Substitute tap/pipe for spoon.
By who and where is this ammended?
The latest edition of the wiring regulations, 411.3.1.2 and 544.1.2.
It might. The house is not their consideration.Their pipe no doubt is earthed in a way satisfoacory to them.
The only way to avoid that is insulating sections to all the pipe work where it is connected to electrical equipment.But now consider the scenario where a fault has developed within the property. Main supply is MDPE so there is no need to cross bond meter connections. Meterman cops it. Likewise main supply is MDPE underground is transitional fitting to steel pipe, up outside wall and 90degree fitting to meter position. that would also become live to anybody touching it, and that length of pipe could be in a public place.
Plumbers do not seem to do that.