I wouldn't say so - he included the word 'standard' (pressure) in his statement.So PBC was wrong, then.
Kind Regards, John
I wouldn't say so - he included the word 'standard' (pressure) in his statement.So PBC was wrong, then.
But if you do not know the frequency then you have no way of knowing the validity of your voltage measurement, just as if you do not know the ambient pressure you cannot be certain that you have measured the boiling point of water correctly.Repeatable in what sense? The water will boil at some specific temperature whatever the pressure, even though that temperature will vary with pressure. The fact that the pressure has altered doesn't affect the accuracy of the temperature measurement taken, it's just that the water is boiling at a different temperature.Thank you PBC. How would you ensure repeatable measurements if the pressure were not specified?
In the same way, while a badly bogged down network which results in a severe drop in supply frequency might well also have the consequences of below-normal voltages, the change in frequency doesn't affect the accuracy with which those voltages may be determined.
Indeed, I'm not seeing the analogy which is trying to be drawn here.This really has nothing to do with what we are discussing. By asking about the boiling point of water you are talking about something which is dependent on something else (pressure). The AC potential difference measured between two points (such as the two conductors of a supply) is in no way dependent on the frequency of that voltage - so it can be measured as accurately and 'repeatably' as one's equipment allows without any knowledge of, or reference to, the frequency - even if that frequency is varying.
I really don't understand your point. Boiling point is dependent on pressure, so you obviously need to know and specify the pressure at which the boiling point has been measured. The voltage of an electrical supply is NOT dependent upon its frequency, so you have no need to know anything about frequency is order to measure, and report, the voltage correctly and accurately.But if you do not know the frequency then you have no way of knowing the validity of your voltage measurement, just as if you do not know the ambient pressure you cannot be certain that you have measured the boiling point of water correctly.
How so? RMS voltage is RMS voltage regardless of frequency. The voltage measured is perfectly accurate and valid whether the grid is supplying exactly 50Hz, 49.5Hz, 50.5Hz, or indeed some frequency outside those limits.But if you do not know the frequency then you have no way of knowing the validity of your voltage measurement
You can be certain you've measured the boiling point of the water at whatever the prevailing pressure happens to be.just as if you do not know the ambient pressure you cannot be certain that you have measured the boiling point of water correctly.
And vice versa.One can still measure the voltage accurately, regardless of its frequency.
Of course you can, but what should the permissible variation of the voltage be?One can still measure the voltage accurately, regardless of its frequency.
The same as at exactly 50Hz?Of course you can, but what should the permissible variation of the voltage be?
That depends upon their intent. If they intend that the voltage limits specified in the regulation always apply, regardless of frequency, then they should remove the phrase "at nominal frequency" from that regulation. If, on the other hand, they intend that there should be different voltage limits for different (ranges of) frequencies, then they simply must 'spell out' those frequency-dependent voltage limits - otherwise we are completely in the dark as to what is required.Of course you can, but what should the permissible variation of the voltage be?One can still measure the voltage accurately, regardless of its frequency.
But you need not be. You have a precise specification of the permissible variation in voltage at a given frequency, and of the permissible variation in frequency. Why would you benefit from a table of voltage tolerances at different frequencies?we are completely in the dark as to what is required.
I'm already agreed with that, but it doesn't alter the fact that either voltage or frequency can be measured separately, without any reference to, or knowledge about, the other.The frequency and the voltage are both closely related to the grid loading, and a few other parameters.
Stating that, for example, "The boiling temperature of water is 100° C" does not have a precise meaning unless the pressure is specified, just as "The supply voltage shall be X ±10%" does not have a precise meaning unless the frequency is specified.I really don't see what analogy you're trying to draw here.
And what useful purpose would that serve?I'm already agreed with that, but it doesn't alter the fact that either voltage or frequency can be measured separately, without any reference to, or knowledge about, the other.The frequency and the voltage are both closely related to the grid loading, and a few other parameters.
As I've just written, IF they want to have different voltage limits at different frequencies, they simply must define what they are.
Kind Regards, John
... because, without such a table, we haven't got a clue as to what what voltage variation is permissible at frequencies which are not 'at nominal' (i.e. 'at', or, at least, very close to, 50 Hz), but which are still within the acceptable frequency range.But you need not be. You have a precise specification of the permissible variation in voltage at a given frequency, and of the permissible variation in frequency. Why would you benefit from a table of voltage tolerances at different frequencies?we are completely in the dark as to what is required.