2391 practical

Discussion in 'Electrics UK' started by alex28, 11 Jul 2008.

  1. alex28

    alex28

    Joined:
    6 Aug 2007
    Messages:
    27
    Thanks Received:
    0
    Country:
    United Kingdom
    anyone got any pictures of fault board scenarios? got 2391 practical on monday and its just the fault board I need to do, passed the other 3 but not being an electrician am struggling to see all the faults on the fault board
     
  2. Sponsored Links
  3. Spark123

    Spark123

    Joined:
    2 Jun 2005
    Messages:
    14,841
    Thanks Received:
    474
    Location:
    Cumbria
    Country:
    United Kingdom
    They are quite obvious faults, you are just doing it as you would an initial verification i.e. look at the conductors, where they are going etc. Make sure the conductors are in the correct connections i.e. polarity. Look at the main bonding, see if it is up to scratch and continuous along its length. Look for RCDs for socket circuits. Check the conductors are tight, not too much insulation stripped back. Check the cables not bent sharply. Check the fuse board schedule is correct and present.
     
  4. alex28

    alex28

    Joined:
    6 Aug 2007
    Messages:
    27
    Thanks Received:
    0
    Country:
    United Kingdom
    Cheers will revise the initial verification stuff in GN3
     
  5. ppuch1

    ppuch1

    Joined:
    8 Aug 2006
    Messages:
    91
    Thanks Received:
    3
    Location:
    London
    Country:
    United Kingdom
    And check for identification of conductors. i.e. colour ident sleeve on any live conductor (switched or otherwise) Strappers colours etc.
     
  6. GaryMo

    GaryMo

    Joined:
    3 Jul 2007
    Messages:
    4,134
    Thanks Received:
    162
    Location:
    Manchester
    Country:
    United Kingdom
    ...and the old favourite - 2 t&e cables on their side clipped together in one cable clip!
     
  7. pompeygit

    pompeygit

    Joined:
    2 Jan 2008
    Messages:
    243
    Thanks Received:
    4
    Location:
    Hampshire
    Country:
    United Kingdom
    And a socket labelled 'outside socket' that has no IP rating, polarity of main tails
     
  8. Sponsored Links
  9. Spark123

    Spark123

    Joined:
    2 Jun 2005
    Messages:
    14,841
    Thanks Received:
    474
    Location:
    Cumbria
    Country:
    United Kingdom
    Think it was labelled for outside use when I did the exam, however it didn't have an RCD (back in the days of the 16th edition) so got noted down. Now of course, if it is to the 17th edition then all normal sockets should be on an RCD.
     
  10. skenk

    skenk

    Joined:
    23 Oct 2007
    Messages:
    1,094
    Thanks Received:
    81
    Location:
    Glasgow
    Country:
    United Kingdom
    I had a damaged cable-entry grommit on mine, just a slice through it you couldn't see it unless you pushed it around.
     
  11. alex28

    alex28

    Joined:
    6 Aug 2007
    Messages:
    27
    Thanks Received:
    0
    Country:
    United Kingdom
    Some of the things are hard to notice-sliced grommet could be difficult to pick up-on the last test they had 1.5mm wire feeding 2.5mm wire but that wasn't a fault?
     
  12. alex28

    alex28

    Joined:
    6 Aug 2007
    Messages:
    27
    Thanks Received:
    0
    Country:
    United Kingdom
    also are the mcb's supposed to be type B? cheers
     
  13. Spark123

    Spark123

    Joined:
    2 Jun 2005
    Messages:
    14,841
    Thanks Received:
    474
    Location:
    Cumbria
    Country:
    United Kingdom
    Why would it be? The 2.5 might be for where the cable is passing through thermal insulation or high ambient etc. It could just be for volt drop, have installed 25mm² tails onto a 70mm² cable for VD before.
    Depends on what the load is really.
     
  14. ColJack

    ColJack

    Joined:
    16 Feb 2007
    Messages:
    11,795
    Thanks Received:
    410
    Location:
    West Midlands
    Country:
    United Kingdom
    mine was general things like..

    no earth sleeving on one of the T+E earths
    no earth wire from the armoured cable banjo
    non continuous wire on the bond from board to water and water to gas ( two cut ends under the earth clamp screw )
    32A breaker on a 2.5 radial
    missing blanks from the knockouts in the board
    neutral from RCD protected circuit in the non rcd neutral block
    earths in wrong terminals on earth block
    twisted T+E
    mains polarity wrong on the incommers ( so all the breakers were then on the neutral )
     
  15. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Loading...

Share This Page