I’m guessing it’s this one.
No real detail only total load = 3.4KW.
No real detail only total load = 3.4KW.
I think I know what you're saying - another toasted FCU.
Are you saying diversity should really only come to play for ovens over 16 amp or so?
We haven't asked/been told what is on the rest of that circuit.
It may be a dedicated oven circuit which just happens to have an FCU?
Or, if it's on the kitchen ring, you may want to keep the washing machine and tumble drier off, until the turkeys done!
...and I would want to use a slightly chunkier flex than 1.25mm2
That is true.
However the heating of the fuse and the plug need to be considered.
The cold resistance of a BS1362 fuse rated as 13 Amp is 0.0075 Ohms and the calculated heat produced in the cold fuse at 16 Amps is 1.9 Watt.
The resistance of the fuse will increase as the temperature of the fuse wire increases and this means that the amount of heat produced will be more than 1.9 Watts.
This may result in damage to plug and/or socket when 16 Amps is flowing for prolonged periods of time.
Sorry, It doesn't make sense to me, But I am not a sparky.
3.4 or 3.6Kw is neither here or there. 200w is negligible here. 2.5mm is fine. for EACH appliance. 3.6KW plus what ever your 2nd oven is (13A?) is over what 2.5mm can carry (16+13A). I think 2.5mm is about 23A, Without 'diversity'. you would need 4mm to your pair of contactors from your 'ring'
You mentioned 'ring' twice. how do you know it is a ring? Is it part of the kitchen sockets or a dedicated cable as a 'radial' with it's own fusing in the CU.
You will need 2 isolators (switches, one for each appliance) to be able to isolate them separately. The 'wall switch would kill them both. Maybe 2 isolators in that cupboard. IF the ovens have their own fuse in the CU, It can be isolated from there, you do not need a wall switch, but can be a pain in the event of an emergency.
Sorry, It doesn't make sense to me, But I am not a sparky.
3.4 or 3.6Kw is neither here or there. 200w is negligible here. 2.5mm is fine. for EACH appliance. 3.6KW plus what ever your 2nd oven is (13A?) is over what 2.5mm can carry (16+13A). I think 2.5mm is about 23A, Without 'diversity'. you would need 4mm to your pair of contactors from your 'ring'
You mentioned 'ring' twice. how do you know it is a ring? Is it part of the kitchen sockets or a dedicated cable as a 'radial' with it's own fusing in the CU.
You will need 2 isolators (switches, one for each appliance) to be able to isolate them separately. The 'wall switch would kill them both. Maybe 2 isolators in that cupboard. IF the ovens have their own fuse in the CU, It can be isolated from there, you do not need a wall switch, but can be a pain in the event of an emergency.
What size is it.Apologies if I am not being clear.
There is a single cooker switch on the wall that has either 4 or 6mm running in to and out of it. That isolates both ovens. The circuit has it's own MCB in the main consumer unit.
Why do you think that. It would be very unusual.I suspect that 4(?)mm then feeds two lengths of 2.5mm T&E that are run as a ring, that is to say, one leg goes to the lower fused spur, the other leg goes to the upper fused spur, there is an additional 2.5mm that runs between each fused spur (thereby creating a ring).
Why do you want MCBs? There is one in the CU though you have not told us the size.AFAIK a single 2.5mm is rated at 27amps (if clipped). If configured in a ring, that goes up to far more than 32amps. I potentially need, as you say, about 23amps.
As things currently stand, each of the inbuilt ovens need to be pulled out (fully) to get to the fused spurs.
I am hoping to change that so that each individual oven can be independently isolated via (dedicated) MCBs in an enclosure in the cupboard space above the two ovens.
To facilitate that, I am now thinking that I will replace both fused spurs with a suitable "connector block" (maintaining the "ring") and run 2.5mm T&E up to each MCB and 2.5mm flex back down to each appliance.
I hope that makes more sense.
What size is it.
Why do you think that. It would be very unusual.
Why do you want MCBs? There is one in the CU though you have not told us the size.
But that is WRONG.I have since removed the fused spur and (in the plastic back box) used 3 way Wago 221 connectors to run some 2.5mm T&E up to an enclosure housing a 16 amp B type MCB. From there I will run 2.5mm flex down to the oven, which I am hoping to lift in to place later this evening.
Why do you say that? It is simply not the case.Any connection to a ring final must be fused at 13amp.
But that is WRONG.
Any connection to a ring final must be fused at 13amp. That is what the FCU is(was) there for. It needs to be reinstated.