    Hi everyone,

    I'm trying to replace my current 3-gang, 1-way switch with a smart switch. The new switch only has one 'live' terminal and three (L1, L2, L3) terminals for each light, whereas my old switch has 3 pairs (1 COM and 1x L1) for each light i.e. 6 terminals altogther.

    I'm aware my old switch doesn't have a neutral, so i've gone for one of the 'no-neutral' smart switches that has a capacitor i need to install on one of the lights.

    My question is how do connect my 6 wires into just 4 terminals on the new switch?

    My current thinking is to wire all 3 COM wires into the one L terminal, then each of the three blue wires into L1, L2, L3 respectively - is this correct?
    Or can i just use any one of the COM wires, and leave the other two disconnected?

    Many thanks for the help!
     

    Attached Files:

  2. Sponsored Links
  3. winston1

    winston1

    Joined:
    11 Jan 2010
    Messages:
    5,355
    Thanks Received:
    382
    Location:
    London
    Country:
    United Kingdom
    The 3 lives could come from different circuits. If so you must not connect them together.
     
    • Like Like x 1
  4. jonnyy2357

    jonnyy2357

    Joined:
    5 Jan 2020
    Messages:
    5
    Thanks Received:
    1
    Country:
    United Kingdom
    Thanks @winston1. If all 3 lights turn off when i flip the same breaker, does that mean they are on same circuit?

    And if so, does that mean i'm ok to join the 3 lives together? Or is better to try leaving 2 of the lives disconnected and just using 1?

    Thank again!
     
  5. Taylortwocities

    Taylortwocities

    Joined:
    28 Jul 2006
    Messages:
    18,764
    Thanks Received:
    1,877
    Location:
    Oxfordshire
    Country:
    United Kingdom
    If they all go off when you operated the MCB, it then sounds that they come from the same circuit. You'll have trouble putting three conductors in the one terminal. You should be ok to use just one of the browns and put the other two in a bit of insulated terminal block to make them safe.

    Do let us know if it works!
     
  6. ericmark

    ericmark

    Joined:
    27 Jan 2008
    Messages:
    14,712
    Thanks Received:
    1,308
    Location:
    Llanfair Caereinion, Nr Welshpool
    Country:
    United Kingdom
    I have 5 switches, only the one with G9 bulbs needs a load capacitor. Mine was a Levante LEVPFCC 4 uf from CEF.
     
  7. jonnyy2357

    jonnyy2357

    Joined:
    5 Jan 2020
    Messages:
    5
    Thanks Received:
    1
    Country:
    United Kingdom
    Update:

    I got it to work by using 1 of the COM wires, and isolating out the other two. All three COM wires were on the same circuit, and i double-checked using a multimeter and testing pairs to the COM wires on the resistance setting and found all three wires were already connected to each other (i.e. the meter had zero restance between any pairs of the COM).

    The capacitor method worked nicely too. The blurb is that without the neutral wire, the switch keeps a low amount of current flowing one of the lights to keep the switch itself powered up (otherwise you'd lose the smart connectivity when all the lights are off). The light that's kept on low power will flicker if using low energy bulbs and the capacitor is used to stop the flickering.

    Once i wired up the switch, i turned it on to see which of the lights flickered before installing the capacitor just to double check which one needed it.

    Pretty happy all round :)
     
    • Like Like x 2
  8. Sponsored Links
  9. Taylortwocities

    Taylortwocities

    Joined:
    28 Jul 2006
    Messages:
    18,764
    Thanks Received:
    1,877
    Location:
    Oxfordshire
    Country:
    United Kingdom
    Cool. Do you have a link for the Wi-Fi switch?
     
  10. jonnyy2357

    jonnyy2357

    Joined:
    5 Jan 2020
    Messages:
    5
    Thanks Received:
    1
    Country:
    United Kingdom
    • Thanks Thanks x 1
  11. seasickstevie

    seasickstevie

    Joined:
    14 Sep 2006
    Messages:
    1,536
    Thanks Received:
    83
    Location:
    Liverpool
    Country:
    United Kingdom
    Thanks jonnyy2357. I see that the capacitor comes included with the switch.

    I've got an old-school touch sensitive dimmer - been in use for some twenty years or more, but since we've 'gone LED' there is the issue of slight flickering when the light's switched off - well more than slight actually. I'm thinking that a capacitor would solve the problem.

    Question: Do you know what value that capacitor is that comes with the MOES?
     
  12. yorkspark

    yorkspark

    Joined:
    6 Mar 2011
    Messages:
    144
    Thanks Received:
    25
    Location:
    Yorkshire
    Country:
    United Kingdom
  13. jonnyy2357

    jonnyy2357

    Joined:
    5 Jan 2020
    Messages:
    5
    Thanks Received:
    1
    Country:
    United Kingdom
    Mine was 0.33uf

    E2ED1997-8DFF-4BBE-BE71-B78BCE3813F3.jpeg
     
  14. Taylortwocities

    Taylortwocities

    Joined:
    28 Jul 2006
    Messages:
    18,764
    Thanks Received:
    1,877
    Location:
    Oxfordshire
    Country:
    United Kingdom
    Danlers have a cheek charging more than £4 for one of those!
    Approx 60p each last time I looked.
     