3 speed extractor fan

Discussion in 'Electrics UK' started by Master of None, 25 Nov 2020.

  1. Master of None

    Master of None

    Joined:
    31 Oct 2007
    Messages:
    425
    Thanks Received:
    21
    Location:
    Edinburgh
    Country:
    United Kingdom
    A friend has built a wooden jacuzzi room in his garden. During use steam is a problem so I suggested an inline extractor. He bought and fitted the fan in the link below.
    EM...M (ruck.eu)
    Being 3 speed and wanting it on full speed only I assumed he would not need the 3 speed controller accessory. So he wired only the Neural and the Line at high speed terminal.
    However it is not performing as expected. I was expecting a room air change every 2 minutes but it has virtually no effect on the steam.
    Is there more to the 3 speed controller than just switching to the low, medium and high terminals in the fan one at a time?
    The documentation is unclear for wiring. The only useful part is below. Full instructions attached.
    It could be it is just not big enough for the job.

    Thank you.
    upload_2020-11-25_22-39-26.png
     

    Attached Files:

  2. Sponsored Links
  3. RF Lighting

    RF Lighting

    Joined:
    31 Mar 2006
    Messages:
    19,990
    Thanks Received:
    1,354
    Location:
    Leeds
    Country:
    United Kingdom
    Is there no better wiring instructions than this? Where did you purchase it from? I have installed multi speed fans before which need links installing to select the speed
     
  4. bernardgreen

    bernardgreen

    Joined:
    3 Nov 2006
    Messages:
    25,588
    Thanks Received:
    2,551
    Location:
    Bedfordshire
    Country:
    United Kingdom
    The extractor extracts air ( and steam ) from the room, there has to be a way to replace the extracted air such as a gap under the door or an air vent. If the room is "airtight" then the fan will not be able to extract air.
     
  5. conny

    conny

    Joined:
    30 Jun 2008
    Messages:
    13,992
    Thanks Received:
    785
    Location:
    Suffolk
    Country:
    United Kingdom
    When you say it is wired between the high speed and neutral only, which terminals have you connected across?
    You may have omitted the run winding connections and be running on the start winding only. If this is the case you may burn it out.
    Alternatively Bernard may have the correct answer that the expelled air is not being replaced quickly enough so steam is not being expelled efficiently.
     
  6. Sponsored Links
  7. Master of None

    Master of None

    Joined:
    31 Oct 2007
    Messages:
    425
    Thanks Received:
    21
    Location:
    Edinburgh
    Country:
    United Kingdom
    He bought it from here. I have attached the instructions for the optional 3 speed switch but it does not really help.
     

    Attached Files:

  8. Master of None

    Master of None

    Joined:
    31 Oct 2007
    Messages:
    425
    Thanks Received:
    21
    Location:
    Edinburgh
    Country:
    United Kingdom
    Yes, he has tried it with various degrees on the roof Velux open. He can feel cold air being drawn in.
     
  9. Master of None

    Master of None

    Joined:
    31 Oct 2007
    Messages:
    425
    Thanks Received:
    21
    Location:
    Edinburgh
    Country:
    United Kingdom
    Wired line to the connection marked High on the fan and Neutral to the one marked N. Because I do not know how the 3 speed switch functions I was wondering if it was--
    Speed 1>low only. Speed 2>Line to low and med terminals. Speed 3>Line to all 3 terminals. Is this likely?
    It could be the fan is too small for the job.
     
  10. conny

    conny

    Joined:
    30 Jun 2008
    Messages:
    13,992
    Thanks Received:
    785
    Location:
    Suffolk
    Country:
    United Kingdom
    I would suggest buying the switch and wiring it correctly through it. That way there can be no doubt it is done correctly rather than guessing which terminal is which on the fan board.
    Bear in mind, this is to ventilate a jacuzzi room where electrical safety should be paramount. Trying to guess where you should connect to isn't really an option.
     
  11. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Loading...

Share This Page