30A fuse not blowing

Joined
24 Nov 2004
Messages
450
Reaction score
7
Country
United Kingdom
An electric shower is pulling 35A.
its circuit is fused with a 30A-rated cartridge fuse.
why isn't the fuse blowing? do I have a faulty fuse?
what fuse should the circuit be protected with?
 
Google “current curves”.

The fuse will likely last many hours with that minor over current. In fact, probably indefinitely.

800px-Curve-BS1361.png
 
Misuse of a circuit like that can cause damage to the fuse holder and fusebox as the fuse will likely be running fairly hot.
 