30A fuse not blowing

Joined
24 Nov 2004
Messages
428
Reaction score
4
Country
United Kingdom
An electric shower is pulling 35A.
its circuit is fused with a 30A-rated cartridge fuse.
why isn't the fuse blowing? do I have a faulty fuse?
what fuse should the circuit be protected with?
 
Sponsored Links
Google “current curves”.

The fuse will likely last many hours with that minor over current. In fact, probably indefinitely.

800px-Curve-BS1361.png
 
Sponsored Links
Misuse of a circuit like that can cause damage to the fuse holder and fusebox as the fuse will likely be running fairly hot.
 