- Joined
- 26 Aug 2016
- Messages
- 6,830
- Reaction score
- 1,009
- Country
Hi all, I was aware DNOs usually have a 2 or 3m rule on tail length, which I assumed for their own reasons (simplicity/flexibility and consistency I guessed). However I was having a read of UKPNs doc and they pin the blame on BS7671 for that rule. That was unexpected.
http://library.ukpowernetworks.co.u...Customer+Supplies+up+to+100A+Single+Phase.pdf
The part of the reg they cite apparently applies only to circuits without adequate *fault* protection.
To determine the adequacy of fault protection purely for BS7671 you would just need the total Zs, the adiabatic parameters for the cables involved and the fuse characteristics?
So it stands to reason that they are saying their fuse doesn't provide adequate fault protection for any length of tails. They are also saying it's not the "overload protection device" for the tails for BS 7671 purposes either.
In that case what is it for? Unspecified DNO protection purposes? Or is it just there to allow meter operators to safely isolate the supply by removing it?
Thoughts?
BS 7671 Regulation 433.2.2 allows a maximum distance of three metres between overload protection devices and their source, therefore the customer shall provide and install an intermediate switch fuse or isolating switch if the distance between the meter and consumer unit is greater than three metres.
Thoughts?