For the power installation on my new build the meter tails and CU are protected by a 100mA RCCD in the meter box. From the day the site was energised this has randomly tripped, often working fine when reset. The electricians have blamed the weather, the equipment in use at the time, the earth strap etc. but on other days, sometimes even just some minutes later, all of these have worked fine. As the build reaches completion we really need this issue fixing and could do with any suggestions what could be the problem, the contractors don't seem to have a clue.
The 30mA RCDs in the CU have never blown. The RCBO can trip with only one socket on one RCD in the CU (how simple can it get). The RCBO unit has been replaced to rule out a faulty unit.
Due to the shape of the building and position of the meter relative to the CU, the meter tails are 10m SWA cable in a duct buried under the floor slab. I had thought that the RCBO was overkill protection of the concealed meter tails cable, it is more than adequately protected by the material of the house. However when I suggested that the RCBO was simply removed I was told this was not safe. The protection was nothing to do with the length of the tails or that they were concealed, but because the resistance provided by our domestic earth rod means that a short in the meter tails could cause 2A to flow in the metal CU while the supply fuse would not trip.
So what is going wrong, and what can be done about it? Are the long tails somehow picking up noise and tripping the sensitive RCBO? How can we get our electrics working reliably? Anyone met anything like this before?
The 30mA RCDs in the CU have never blown. The RCBO can trip with only one socket on one RCD in the CU (how simple can it get). The RCBO unit has been replaced to rule out a faulty unit.
Due to the shape of the building and position of the meter relative to the CU, the meter tails are 10m SWA cable in a duct buried under the floor slab. I had thought that the RCBO was overkill protection of the concealed meter tails cable, it is more than adequately protected by the material of the house. However when I suggested that the RCBO was simply removed I was told this was not safe. The protection was nothing to do with the length of the tails or that they were concealed, but because the resistance provided by our domestic earth rod means that a short in the meter tails could cause 2A to flow in the metal CU while the supply fuse would not trip.
So what is going wrong, and what can be done about it? Are the long tails somehow picking up noise and tripping the sensitive RCBO? How can we get our electrics working reliably? Anyone met anything like this before?