Have your lecturer go through it with you, basically unplug everything, isolate and disconnect the L&N at the consumer unit, IR test @ 500v between L&E and N&E.
Just to clarify what Mr. 123 said, if you are testing a circuit that you are not 100% sure about, you should test it between live and neutral tied together to earth, testing them separatly to earth can give issues, if for example you tested at 500v betwene live and earth and the circuit had a neutral to earth fault, the 500v would appear between live and neutral and could do some damage!