miajanjua said:The diversity for a cooker is 10A + (1/3 x Total Cooker Amps)
6.8Kw+3.8Kw = 10.6Kw Giving a current of 46 Amps @ 230V
After Diversity the Design Load for the cooker is 10+1/3x46 = 25.3Amps
6mm2 Cable is rated @ 32Amps
So well in access to what is required to supply the Hob and the oven together!!!
![]()
securespark said:miajanjua said:The diversity for a cooker is 10A + (1/3 x Total Cooker Amps)
6.8Kw+3.8Kw = 10.6Kw Giving a current of 46 Amps @ 230V
After Diversity the Design Load for the cooker is 10+1/3x46 = 25.3Amps
6mm2 Cable is rated @ 32Amps
So well in access to what is required to supply the Hob and the oven together!!!
![]()
Seeing as we are slagging each other off regarding their mathematical conclusions, yours are off the mark, too.
The equation is: 1st 10A+ 30% of remainder + 5A for s/outlet.
Could not agree more.. It sounds to me that this job is not really DIY and that an electrician should be called in.
your 6mm will be fine
It is better not to apply much diversity to domestic cookers, because at times (e.g. cooking Christmas dinner) you will have all the rings and oven full on. When you first turn them on they use full current until they reach temperature and the thermostats start to cycle.