I need to extend the lenght of 6mm cable by joining under floor boards what type of jointing would you recomend
http://www.tlc-direct.co.uk/Products/WA173.html
http://www.tlc-direct.co.uk/Products/WAGOBOX.html[/QUOTE]
If the junction box is inaccessible then this combination will not meet the requirements of BS7671.
Furthermore, you will not fit two 6mm cables in the wago.
You will either have to make the junction box accessible or consider crimping the cables together using the appropriate equipment. I.e. a ratchet crimper.
Furthermore, you will not fit two 6mm cables in the wago.
...... or consider crimping the cables together using the appropriate equipment. I.e. a ratchet crimper.
What kind of crimps would be used for crimping two T&E cables together? Would normal yellow butt crimps be appropriate?Sherbertlion said:You will either have to make the junction box accessible or consider crimping the cables together using the appropriate equipment. I.e. a ratchet crimper.
What kind of crimps would be used for crimping two T&E cables together? Would normal yellow butt crimps be appropriate?
I know the connector you linked to is rated at 41A and should have been tested to carry that current so I guess I should have more faith but I'm struggling!
NIC assessors have said to me that they are happy for me to sign EICs saying that my work complies with BS 7671 even though it doesn't
http://www.tlc-direct.co.uk/Products/WA173.html
http://www.tlc-direct.co.uk/Products/WAGOBOX.html[/QUOTE]
If the junction box is inaccessible then this combination will not meet the requirements of BS7671.
Furthermore, you will not fit two 6mm cables in the wago.
You will either have to make the junction box accessible or consider crimping the cables together using the appropriate equipment. I.e. a ratchet crimper.
http://www.tlc-direct.co.uk/Products/WA173.html
http://www.tlc-direct.co.uk/Products/WAGOBOX.html[/QUOTE]
If the junction box is inaccessible then this combination will not meet the requirements of BS7671.
Furthermore, you will not fit two 6mm cables in the wago.
You will either have to make the junction box accessible or consider crimping the cables together using the appropriate equipment. I.e. a ratchet crimper.
No - but the point I was making was that if you did then apparently NICEIC would be happy for you to sign an EIC...I didn't say I have, or would use them in a 'maintenance free' capacity.