80A PME Fuse

My I remind us that when some rule or reg or law states some particular thing - in this case being the csa of a particular conductor - it does not invarably mean you may not use something better by some reason ...
Sure - the sort of regs we're talking about always dictate minimum requirements, and there is rarely, if ever, anything wrong with 'exceeding' those minimum requirements.

However, if, BS7671 says that a certain conductor must have a minimum CSA of, say, 16mm², I don't see in what sense a DNO could argue that 10mm was 'better' (or even 'adequate') :-) Am I missing something?
 
Regarding upgrading 80-100a fuses, in SSE DNO areas at least, 100a cutout fuses are no longer permitted, if found they have to be changed to 80a on domestic installations. This is to protect the metering and customers equipment from overload as 100a fuses can withstand much higher load than 100a for a long time which could lead to damage/fire. This came about because of additional loads with all the EV and heat pumps being put in these days.
An 80a fuse will blow before things get dangerously overloaded.
UK should fit separate consumer main overload protection at the DNO fuse location

DNO fuse for disconnection and short circuit protection only
 
I am still confused.

Right, so I had exactly the same thoughts over a decade ago :-)
Did you?

For example:
Adiabatic calculation, 13mm²
Table 54.7, 16mm²
Table 54.8, 10mm²

When you write:

For non-PME, the minimum CSA of Earthing Conductor is given by (adiabatic calculation OR Table 54.7)
For PME, the minimum CSA of Earthing Conductor is given by the higher of (adiabatic calculation OR Table 54.7) AND (the CSA required for a PME main bonding conductor as given in 54.8 ).


Did/does that not mean that in both cases the CSA of EC shall be 16mm²?
 
I am still confused. ....
For example: Adiabatic calculation, 13mm² ... Table 54.7, 16mm² .... Table 54.8, 10mm²
When you write:
For non-PME, the minimum CSA of Earthing Conductor is given by (adiabatic calculation OR Table 54.7)
For PME, the minimum CSA of Earthing Conductor is given by the higher of (adiabatic calculation OR Table 54.7) AND (the CSA required for a PME main bonding conductor as given in 54.8 ).

Did/does that not mean that in both cases the CSA of EC shall be 16mm²?
Yes, with those figures it would mean that.
However, Table 54.7 is only relevant if one does not want to undertake the adiabatic calculation, so one can ignore it if, as in your example, the calculation has been done. However (2), since your adiabatic calculation has indicated the need for at least 13mm², in practice that obviously means 16mm² cable.

However (3), if your adiabatic calculation had resulted in a figure of, say, 9mm², then 10mm² cable presumably would (per Table 54.8) be adequate for an Earthing conductor, regardless of (the irrelevant) Table 54.7
 
Yes, with those figures it would mean that.
However, Table 54.7 is only relevant if one does not want to undertake the adiabatic calculation, so one can ignore it if, as in your example, the calculation has been done.
Agreed.

However (2), since your adiabatic calculation has indicated the need for at least 13mm², in practice that obviously means 16mm² cable.
Agreed.

However (3), if your adiabatic calculation had resulted in a figure of, say, 9mm², then 10mm² cable presumably would (per Table 54.8) be adequate for an Earthing conductor, regardless of (the irrelevant) Table 54.7
Agreed.

BUT -

this all started because you said the Earthing conductor could be 10mm² with 25mm² tails.
And a 16mm earth, they were most concerned about that when ours was upgraded!
That presumably is a rule of their own?

As far as BS7671 is concerned, even with a 'PME' (TN-C-S) supply, Earthing and Main Bonding conductors only have to be greater than 10mm² if the incoming PEN is bigger than 35mm² - which I imagine is very rare in a domestic installation.
So, which is it?
 