I'm starting to wonder whether you have understood my questions and the thinking behind them ...
... the 'customer-side' can do nothing about 'protecting' the meter or anything upstream of it. All of the final circuits in the installation should be adequately protected (against both overloads and 'faults') by the devices (MCBs or RCBOs) in the CU. That only leaves the connection between meter and the devices in the CU (i.e. 'tails' and Main Switch') and, as I mentioned (which started this bit of the discussion), DNOs will usually only upgrade their fuse to 100A if those tails are at least 25mm², since (like BS7671) they don't believe that cables any smaller than that would be adequately protected by a 100A fuse.
Hence, if the DNO fuse is 100A, the meter tails are 25mm², the Main Switch rated for100A and the rest of the installation correctly designed and installed, it would seem that absolutely everything will be adequately 'protected' (against both overload and 'faults').
That's the reason why I've been asking what you feel needs further "overload protection", given that, as above, it would seem that everything would already be appropriately 'protected'. I'm therefore wondering whether you perhaps don't actually mean 'protection' in the usual sense but that you are, rather, referring to "current limitation", which is not something we do explicitly in this country - at least, not in domestic installations?
Kind Regards, John