Adding sockets to downstairs ring main.

kitchens require 2 or more radials rather than a ring..
one 20A radial for general sockets, one suitably sized radial for the cooker circuit, and one 16A radial for each of the major current using appliances ( WM, DW, TD, IWH etc ).
possibly you could use one 20A or 25A radial for 2 appliances but an assesment of usage would need to be carried out. will you be likely to use the 2 appliances at the same time? etc
 