kitchens require 2 or more radials rather than a ring..
one 20A radial for general sockets, one suitably sized radial for the cooker circuit, and one 16A radial for each of the major current using appliances ( WM, DW, TD, IWH etc ).
possibly you could use one 20A or 25A radial for 2 appliances but an assesment of usage would need to be carried out. will you be likely to use the 2 appliances at the same time? etc
one 20A radial for general sockets, one suitably sized radial for the cooker circuit, and one 16A radial for each of the major current using appliances ( WM, DW, TD, IWH etc ).
possibly you could use one 20A or 25A radial for 2 appliances but an assesment of usage would need to be carried out. will you be likely to use the 2 appliances at the same time? etc